Thread: Daikin vrf with com's issue
-
07-10-2015, 07:39 PM #1
Daikin vrf with com's issue
Hi guys.
I've been called out recently to some Daikin vrf systems with com's fault "ue".
There is a main centralised controller which is controlling everything.
On the controller it is controlling 3 vrf systems.
System 1 is running fine but the other 2 systems are not working.
All indoors are showing on the I touch main controller but are not able to be turned on or so anything.
Is checked com's between controller and outdoors and getting 16dc v on the com's.
Getting 16dc v to the indoors
But not getting anything on the multi link from one outdoor to the other.
I've tried resetting everything but no joy.
If anyone could help it would be appreciated
Cheers
Dean
-
10-10-2015, 09:54 AM #2
Re: Daikin vrf with com's issue
Search dead MB in indoor unit.
-
10-10-2015, 11:40 AM #3
Re: Daikin vrf with com's issue
centralised connects accross outdoor units
-
08-11-2015, 04:44 PM #4
Re: Daikin vrf with com's issue
dead MB???
-
09-11-2015, 05:17 AM #5
Re: Daikin vrf with com's issue
try Daikin Tech Support , they are very helpful in Australia. Don't know if they have the support in England that we get in Aust.
-
10-11-2015, 06:20 PM #6
Re: Daikin vrf with com's issue
Try 01275 341030 Daikin uk support. Usually very helpful.
-
16-11-2015, 06:44 PM #7
Re: Daikin vrf with com's issue
Check the F1-F2 terminals labelled OUT on each master VRV system, if you have system 1 with no coms then the cable from central probably goes to this on the correct terminals, from these terminals follow the cable to the next system and then the next but remember if one system has two outdoor units only work on the masters