    I M I Celler cooling



    Good day everybody. I don't know if you can help. I have just been to a imi Celler cooler.with a cu 50 2hp outdoor unit on r 22. Does anyone know what the expansion device is on these.it is about 10 years old.when it's running there is some sort of fitting on the liquid line after the drier just as it goes into the evaporator and it is frosting from there into the evaporator. Is this normal.cheers.



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: I M I Celler cooling

    That's normal. It's called a bullet tube restrictor. There's a gauze to catch the crud then an insert with a small hole which is where liquid refrigerant expands. You might find a different size one taped inside the outdoor unit which gets used on the system depending where the device is and pipe run if I remember correctly.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: I M I Celler cooling

    Remember, it's R22, so you can't touch it easily.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: I M I Celler cooling

    Many thanks tayters.not come across that before.typical imi.cheers. Pete

  5. #5
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: I M I Celler cooling

    Aye.all good things have gone now.enjoy your retirement and go fishing.you can paint the house later.

  6. #6
    Join Date
    Dec 2008
    Location
    england
    Age
    77
    Posts
    137
    Rep Power
    16

    Re: I M I Celler cooling

    Hi andy.have you any idea of the refrigerant charge for these systems.pipe run about 15mtrs of 5/8 + 3/8 pipe

  7. #7
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: I M I Celler cooling

    Not sure on that one, stick 2kg in the F Gas log book ha ha.

    Think the idea is to fit the larger orifice by the outdoor unit if you have a longer pipe run and lag the 3/8" pipe or something along those lines at least.
    Found the sight of those things seem to defy logic. Warm pipe one side, cold on the other, can't argue with the laws of thermodynamics though, all that crazyness going on in such a short distance.

    Cheers,
    Andy.