Fault in York Ec 500
Hi brother
I have one chiller Ec 500 York ( york millenuium chiller ).
The fault is low curre/mp/hp
In the system no:1
And others system working no problem
NB : I hear some noise in the first contactor for (star delta)
I hope I can find some help like evry time I share my proplem with you
Sorry for my bad English
-
27-09-2015, 10:18 PM #2
Re: Fault in York Ec 500
Check the contactors are getting voltage, check the auxillary contacts on the first (main) contactor
Mostly found in the southern part of this green and pleasant land.
-
28-09-2015, 02:39 PM #3
Re: Fault in York Ec 500
Thanks bro to help
After checking I will tell you the results