    Unhappy Mitsubishi Electric Vrf problems with one indoor unit.



    Hi Everyone
    I have a problem with a
    Mitsubishi Electric VRF system.
    Model No PEFY-P32VMA-E
    Ser No 2K02997
    So the this system has 9 indoor units on all the other units hold temp.
    But this this one doesnt.
    This is the third time something has gone wrong and im not sure why it keeps doing this.
    When i have spoke to Mitsubishi in the past we have focused on the lev head.
    The head was replaced first time around and was working fine.
    About two weeks ago it stopped performing and coulnt hold temp.
    So i tried a lev head reset by disconnecting the m net etc and resetting that worked again and worked very well was really chuffed.
    But two three weeks down the line the room is not holding temp again but all the other units are.
    Does anyone know any common faults ??????
    Could it be comms errors ?????
    Could it be bc box fault ?????????
    Could it be bc box port,comms fault
    To be honest im stuck and at the hands of the gods and Mitsubishi

    Ian



  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Mitsubishi Electric Vrf problems with one indoor unit.

    Hi Ian,

    Have you checked the port address at the indoor and confirmed its connected to that port at the BC box? Check the indoor thermistors are reading correctly. Is it just one indoor connected to one remote controller? Check where the indoor is using the return air sensor from. Ie back of the unit, remote or wall sensor. Is the indoor calling for heating/ cooling or is the return air sensor in a poor location.

  3. #3
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17

    Re: Mitsubishi Electric Vrf problems with one indoor unit.

    Hi Neddy

    Back on this one again this is the most annoying fault I think I have ever had so fed up.
    Same faults again been speaking to Mitsubishi been getting different ideas keep getting different engineers don't think they believe me or understand the fault or situation im in.
    But changed the settings to the thermistor on the controller as well now.
    Been speaking again they think the Lev head is Faulty again so ive taken it off and checked the spindle.
    they said if its not flush with the oring and driven out when taken off its faulty.
    And that it must of been over tightened when put on he said hand tight then 1/4 of turn with spanners the maximum im pretty much I done what I was told but cant be sure.

    Can anyone tell me if they have had this problem before ?
    Any Mitsu specialists ?
    Also does anyone have the correct procedures in there notes for fitting them.
    Ie powering down the system ie cond indoor unit bc boc etc.
    Please help ahhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhh lol
    I need a pint soon
    peace my rant is over lol
    please help

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Mitsubishi Electric Vrf problems with one indoor unit.

    Tim Keywood