Results 1 to 14 of 14
Thread: R290 Systems
    Mar 2006
    Frederikssund
    43
    Thumbs up R290 Systems
    I like to see all types of R290 systrems that you have experince with
    Chillers, Oil return, exp valv, exp systems,level controls, drive conditions.
    Our Product program
    Chiller
    evap: Plate
    cond: Plate/Aircondenser
    exp:danfoss exp valve
    55 Kw-330kw @ 0C/35C
    No oil return
    Aug 2005
    5,327
    Re: R290 Systems
    Flooded shell & tube evaporator + flash tank + two engine driven twin screw compressors + air cooled oil coolers for natural gas processing facility
    recip. compressors + air-cooled condenser + thermosiphon oil & head cooling for off-shore platform used to cool a membrane for CO2 removal from natural gas supply
    Gas compression compressor (twin-screw & propane) all explosion proof for gas processing facility
    Just to name a few...
    All were intrinsically safe.
    Mar 2005
    70
    639
    14
    Re: R290 Systems
    Gas engine drives, steam turbine drives as well as electric motor drives. Air cooled condenser, water cooled condensers and evaporative cooled condensers.
    I had used oil flooded twin screw compressor, recip compressors and centrifugal compressor, ranging from 50 HP up to 6500 HP.
    Most all are Class 1, group C&D, Division 2 area classification and a few are Division 1.
    The smaller units are skid mounted and factory assemblied and the larger ones are partially field erected.
    The uses are in gas processing facilities, refineries and chemical plants. Most are due to having propane in the plant as a normal part of the process. many do not use refrigerant grade and use HD-5 grade of propane as it is more readily available. The HD-5 grade is about 95% propane and has some light ends and some heavy ends. The light ends effect the partial pressure and cause a higher than normal condensing pressure which draws more HP in the compressor.
    A few projects are also on propane storage caverns, propane barges and propane land based storage facilities. We also have propane refigeration/recovery equipment on off shore production platforms.
    Ken
    SANJEEV KUMAR's Avatar
    SANJEEV KUMAR Guest
    Re: R290 Systems
    procedure to charge hc blend in r12 refrigerator and operating pressure of the same.
    Mar 2005
    70
    639
    14
    Re: R290 Systems
    I don't understand your question?
    Ken
    Jan 2006
    Croatia
    2,136
    Re: R290 Systems
    Hi, Sanjeev Kumar
    Quote Originally Posted by SANJEEV KUMAR View Post
    Are you asking about retrofit R12 system with another refrigerant (R134a)
    http://www.shoptrac.com/r12retro.htm
    http://www.google.com/url?sa=t&ct=re...5cA3t05YeQI8Ww
    Best regards, Josip
    Australia
    33
    73
    12
    Re: R290 Systems
    Hydrocarbon Link of interest
    click into Hr12 for a tempreture pressure chart
    for the r12 replacement
    http://www.hychill.com.au/tech/
    Jan 2009
    INDIA
    40
    Re: R290 Systems
    have u dealt with Propylene ,proapane and ethylene mixture ? Normally pure propane is difficult to get in refineries.
    Jan 2009
    INDIA
    40
    Re: R290 Systems
    How did you solve the problem of set points of instruments,in plant ,running on propylene blended mixtures as well on 95 % propane? actually customer wants to run the plant on both types of hydrocarbons.
    Dec 2008
    36
    58
    10
    Re: R290 Systems
    I have none but would like to learn because it seems that the industry may be heading in the HC arena in the next few years. I'm in the US and it hasn't become popular yet but i'm sure will soon enough. Some of you out there are from places where HC is commonly used, I wonder how to do you recover these types of refrigerants?
    Sep 2008
    Philippines Islands
    27
    Re: R290 Systems
    Hello, I red your posts, definitively interesting.
    I was asking myself a basic question:
    because of flammable and explosive nature of R290, which is the
    - maximum pressure
    - maximum temperature
    a component should respect to respect a safety limit and avoiding issues of flaming and explosion ?
    Many thanks
    Jan 2006
    Croatia
    2,136
    Re: R290 Systems
    Hi, PaulL
    Quote Originally Posted by PaulL View Post
    - maximum pressure
    Many thanks
    R290 - propane is used as refrigerant (must be very pure) thus in closed circuit .... suction and condensing pressure/temperature are between
    Tmin= -56*C and critical T= 96*C
    Equipment used (electrical motors, switches etc.) must be EEX-explosion proof... thus no problem with fire and explosion....
    Best regards, Josip
    Sep 2008
    Philippines Islands
    27
    Re: R290 Systems
    Many thanks Mr. Josip.
    As a matter of fact, I was not clear enough.
    Please let me put the question in a different way.
    Ex: is R290 safe at 30 bar and corresponding saturation temperature (77.5 C) or may be present any hazard of explosion ?
    What worries me is: according to what rule a component supplier (valves, heat exchanger, compressors) declares these values ?
    Many thanks
    Jan 2006
    Croatia
    2,136
    Re: R290 Systems
    Hi, PaulL
    Many thanks
    Refrigeration plants (where I was working) were working with lower value both temperature&pressure, but I believe when we are bellow critical T= 96*C and critical P=42 bar we are in safe area
    autoignition temperature is around 450*C
    please check this..
    http://docnav.grasso-global.com/.../...290_gbr_1_.pdf
    Best regards, Josip
  1. contaminants in ammonia systems
    By Johnny Rod in forum Refrigerants
    Last Post: 17-10-2011, 05:26 PM
  2. R290?
    By andyh in forum Refrigerants
    Last Post: 22-09-2007, 06:42 PM
  3. My local Apprentice Training Classes
    By shogun7 in forum Training
    Last Post: 17-03-2007, 03:10 PM
  4. Refrigeration alarm systems
    By tonydeith in forum Supermarket Refrigeration
    Last Post: 27-04-2006, 01:43 AM
  5. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Last Post: 21-04-2006, 10:02 PM