Results 1 to 9 of 9
    Jul 2014
    Italy
    5
    Single stage -40 C
    Hello, I have a small fridge and I need 1,5 kW of refrigeration power when it's temperature is -40C. What kind of gas would you use?
    I tried with R404A, but the temperature can't reach -40C.
    Any idea?
    Thank you!
    Sep 2003
    ISRAEL
    66
    4,173
    40
    Re: Single stage -40 C
    first you need a compressor that can reach -40, I would suggest R-507 or R-410A.
    Jul 2014
    Italy
    5
    Yes, it was the following question
    What compressor should I use?
    Sep 2003
    ISRAEL
    66
    4,173
    40
    A compressor with 1.5 KW capacity at -45C evaporating temp.
    Jul 2014
    Italy
    5
    Yes, but I didn't find anything with this specs. Can you suggest me something? (reciprocating or scroll)
    Sep 2003
    ISRAEL
    66
    4,173
    40
    Check Bitzer and Copeland semi hermetic two stages low temp.
    Oct 2003
    56
    5,519
    28
    CO2 machine Bitzer, Dorin..
    Nov 2009
    Minsk, Belarus
    33
    164
    9
    I think 1.5 kW capacity at -47C evaporating temperature... and it's may be two stage semihermetic compressor on R507/404
    In some places will have to think ...
    Mar 2009
    U.S.A.
    300
    13