One of our service techs said he had a high pressure (HPC) tripping at 275# (18.9 bar) when the HPC was set for 425# (29.3 bar). The system is R-22.
He said the cause was flood back causing scroll plate separation then the reverse flow of the discharge gas to the compressor caused a hammer effect on the HPC causing it to trip.
This problem occurs specifically as the fan cycle control (FCC) cycles on with with FCC bypassed there is no problem.
Other info: 65# (4.4 bar) suction, 275# head, 2* (1.1*C) superheat, 12* (6.6*C) sub cooling, no rapid equalization as if a pop-off goes off, this is a new 7.5 ton condensing unit on an existing air handler w/TXV, Copeland Compliant Scroll.
I know the 2* (1.1*C) SH too low taking action to rectify that, Replacing the Air Handler like we should have done to start with.
I'm not bitting on the hammering of the HPC, I believe there is some type of restriction in the condenser or its outlet that he is not seeing.
Any ideas or conformations?
Has any one heard of plate separation (compliance) causing a situation like this?
SteveLast edited by Steve Wright; 01-05-2006 at 07:21 PM. Reason: SI conversion
27-04-2006, 09:37 PM #2
Re: Copeland scroll compressor
Is it possible to place SI units between brackets please?
This is very difficult to read for SI readers.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
27-04-2006, 11:47 PM #3
I cannot help but think that your problem will disappear as soon as you get your superheat under control.
28-04-2006, 02:54 PM #4
Hey Dan
No i am not confident of that relationship tripping HPC vs FCC on however the problem went away when we stopped the FCC from cyling.
I think there is a restriction at the outlet of the cond and that is what the FCC looks at.
When we change the air handler I'll cut in a tee.
Steve
28-04-2006, 02:55 PM #5
Peter
That is a good idea do you know a quick source for conversion to SI, is there one on this site?
Steve
28-04-2006, 03:14 PM #6
Originally Posted by Steve Wright
for me this one is the best:
http://ns.winsite.net/bin/Info?2156
but you can choose:
http://www.katmarsoftware.com/uconeer.htm
http://www.sporlan.com/unitconverter.htm
Agree with Peter_1, quys please put in brackets SI values
Best regards,
Josip
29-04-2006, 04:07 AM #7
29-04-2006, 04:30 AM #8
transfer to SI
HPC 275 ---18.9bar
425----29.3bar
suction 65---4.48bar
head---18.9bar
SH=1.1K
SC=6.6K
if offer a sketch of control of FCC and HPC, it's better to know the problem
rgds
LCI hear...I forget;I see...I remember;I do...I understand
01-05-2006, 07:11 PM #9
Dan
I'm thinking the liquid line is at a much lower pressure than the condenser pressure.
The HPC is at the inlet of the condenser and the FCC is at the outlet of the condenser.
I will let you know what I find.
Steve
01-05-2006, 07:13 PM #10
Many Thanks to Josip and LC for SI conversion.
Steve
can overfilling/overcharging damage a compressor?
By fredjchavez in forum Trouble ShootingReplies: 10Last Post: 12-02-2009, 10:30 AM -
Compressor pumping efficiency
By shogun7 in forum FundamentalsReplies: 0Last Post: 25-02-2004, 10:50 PM -
One Half of a Part Wound Compressor Motor is Burnt
By aygul in forum Trouble ShootingReplies: 2Last Post: 25-08-2003, 11:11 AM -
Compressor failure...... cause
By herefishy in forum Technical SpeculationsReplies: 8Last Post: 06-12-2002, 12:15 AM -
Starting a compressor, and receiver questions.
By DaBit in forum Technical SpeculationsReplies: 9Last Post: 24-08-2002, 12:37 PM