    Copeland scroll compressor



    One of our service techs said he had a high pressure (HPC) tripping at 275# (18.9 bar) when the HPC was set for 425# (29.3 bar). The system is R-22.

    He said the cause was flood back causing scroll plate separation then the reverse flow of the discharge gas to the compressor caused a hammer effect on the HPC causing it to trip.

    This problem occurs specifically as the fan cycle control (FCC) cycles on with with FCC bypassed there is no problem.

    Other info: 65# (4.4 bar) suction, 275# head, 2* (1.1*C) superheat, 12* (6.6*C) sub cooling, no rapid equalization as if a pop-off goes off, this is a new 7.5 ton condensing unit on an existing air handler w/TXV, Copeland Compliant Scroll.

    I know the 2* (1.1*C) SH too low taking action to rectify that, Replacing the Air Handler like we should have done to start with.

    I'm not bitting on the hammering of the HPC, I believe there is some type of restriction in the condenser or its outlet that he is not seeing.

    Any ideas or conformations?

    Has any one heard of plate separation (compliance) causing a situation like this?

    Steve
    Last edited by Steve Wright; 01-05-2006 at 07:21 PM. Reason: SI conversion



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Copeland scroll compressor

    Is it possible to place SI units between brackets please?
    This is very difficult to read for SI readers.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Copeland scroll compressor

    This problem occurs specifically as the fan cycle control (FCC) cycles on with with FCC bypassed there is no problem.
    Hi Steve. This is very odd, indeed. Are you confident that there is a relationship between cycling the fans ON and not OFF? I would put a tee at the high pressure control and see what the gauges say.

    I cannot help but think that your problem will disappear as soon as you get your superheat under control.

  4. #4
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Copeland scroll compressor

    Hey Dan

    No i am not confident of that relationship tripping HPC vs FCC on however the problem went away when we stopped the FCC from cyling.

    I think there is a restriction at the outlet of the cond and that is what the FCC looks at.

    When we change the air handler I'll cut in a tee.

    Steve

  5. #5
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Copeland scroll compressor

    Peter

    That is a good idea do you know a quick source for conversion to SI, is there one on this site?

    Steve

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Copeland scroll compressor

    Quote Originally Posted by Steve Wright
    Peter

    That is a good idea do you know a quick source for conversion to SI, is there one on this site?

    Steve
    Hello Steve,

    for me this one is the best:

    http://ns.winsite.net/bin/Info?2156

    but you can choose:
    http://www.katmarsoftware.com/uconeer.htm
    http://www.sporlan.com/unitconverter.htm

    Agree with Peter_1, quys please put in brackets SI values

    Best regards,

    Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Copeland scroll compressor

    I think there is a restriction at the outlet of the cond and that is what the FCC looks at.
    What is the High pressure safety control looking at? If there is a restriction at the outlet of the condenser, wouldn't the FCC see the same pressure as the high pressure safety control?

  8. #8
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Copeland scroll compressor

    transfer to SI

    HPC 275 ---18.9bar
    425----29.3bar

    suction 65---4.48bar
    head---18.9bar

    SH=1.1K
    SC=6.6K

    if offer a sketch of control of FCC and HPC, it's better to know the problem

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  9. #9
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Copeland scroll compressor

    Dan

    I'm thinking the liquid line is at a much lower pressure than the condenser pressure.

    The HPC is at the inlet of the condenser and the FCC is at the outlet of the condenser.

    I will let you know what I find.

    Steve

  10. #10
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19

    Re: Copeland scroll compressor

    Many Thanks to Josip and LC for SI conversion.

    Steve

Similar Threads

  1. can overfilling/overcharging damage a compressor?
    By fredjchavez in forum Trouble Shooting
    Replies: 10
    Last Post: 12-02-2009, 10:30 AM
  2. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  3. One Half of a Part Wound Compressor Motor is Burnt
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 25-08-2003, 11:11 AM
  4. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •