    York YCA 60 9Si 50A chiller



    We have got the opportunity to decommission one of these chillers, unfortunately we have not been able to get to the site to check the details.
    York are being their normal careful with releasing the requested information.
    Does anyone have any data with regards the amount of refrigerant that may be in this chiller please?


    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  2. #2
    Join Date
    Jul 2012
    Location
    England
    Age
    59
    Posts
    4
    Rep Power
    0

    Re: York YCA 60 9Si 50A chiller

    There should be an additional letter after the YCA, probably an F given the rest of the data, although you'll probably find the 9 should be a G. Have no manuals on an AF but based against similar York 60 Ton machines your looking at around 50Kg. Trust this helps

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: York YCA 60 9Si 50A chiller

    Thanks Jim, that's great.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.