    Angry What refrigerants is inside?



    It is a WIF. Recently I have welding repaired the condensing unit for that. So much gas leaked away, there is not enough gas inside. But I couldn't figure out the refrigerants inside.

    It is Hussmann condensing unit. The attached label indicate it is R12 unit. But I found compressor is R502 unit(model: Copeland semi hermetic, EAD1-0200-TAC), and also found TXV is GRE-1-ZP(R404, 507, 502). There is Large printed letter on c/u - R12".

    I wonder if there is R12 or R502 inside the unit!
    I am lost. Please help me with this matter.
    R12 can be used for R502 compressor with R502 TXV?.
    It is low temp unit and worked well for 15 years with almost no issue.



  2. #2
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: What refrigerants is inside?

    Check pressure & outside temperature.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: What refrigerants is inside?

    You cannot use R12 any more, it is illegal.

    Match the TXV gas.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jun 2008
    Location
    Canada
    Posts
    72
    Rep Power
    16

    Re: What refrigerants is inside?

    Can you get R12? It was stopped production 20 years ago.
    Pressure wise it seems R12. TXV is R404/R02. but I cannot ignore the nameplate of manufacturer too, that is R12.

  5. #5
    Join Date
    Jun 2008
    Location
    Canada
    Posts
    72
    Rep Power
    16

    Re: What refrigerants is inside?

    I've forgot , low 25~ psi, high 200 psi. box temp 35 F, sight glass: 1/2 stable and clear with barely moving.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: What refrigerants is inside?

    Being low temperature application, the TXV being R404A/R502 and the compressor similarly so all points to it having R404A or R502 in it originally. The rest of the condensing unit won't care what refrigerant it has in it so long as its components are rated for the pressure and duty.

    Pump the system down, disconnect the compressor electrically but run the condenser fans till the condenser and receiver reach ambient temperature, measure the refrigerants pressure and look it up on a PT chart, it will point you in the right direction as to what is in there.

    It would make sense to recover and start again with a fresh charge.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Jun 2008
    Location
    Canada
    Posts
    72
    Rep Power
    16

    Re: What refrigerants is inside?

    I have recovered all the gas inside and freshly charged R422A. It works fine till present. Thanks.

  8. #8
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0

    Re: What refrigerants is inside?

    now you have another problem, tell the supplyhouse what the gas is...They wont kow and will wack you good to dispose of the stuff. keep the cylinder in the house or basement with a thermometer for a day and then read the pressure of the cylinder. compare it to a PT chart to ID thje gas. It is likely 502 if its low temp(freezer). R12 started phasing out 7/92 and 502 not long after.
    My wife says I don't listen to her....or something like that....

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •