    Problems in thermo king sl 200



    Hi Guys
    There is a problem
    First: emptied humidity and air by vacuum pump and began Charged *****
    Official quantity 6.35 kg but after Charged 3.5 kg
    high pressure 300 and low pressure of more than 120
    Second: engine speed does not go up
    Bunny logo on the screen does not appear

    thermo king SL 200
    thermoGuard VI b

    Greetings



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Problems in thermo king sl 200

    That suction is way way too high,you need to pump down that system try closing the suction on the compressor if that's pulls a good vac then open it and close the outlet from the receiver tank something is badly wrong with the unit,the throttling valve should limit if you are getting that kind of pressure at the suction you have a major issue

  3. #3
    Join Date
    Nov 2012
    Location
    EYGPT.DAMITTA
    Posts
    37
    Rep Power
    0

    Re: Problems in thermo king sl 200

    Throttling valve replaced. But there is no improvement. Low pressure throttling valve 160 and bottom throttling valve 20 What are your expectations for that problem

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Problems in thermo king sl 200

    Three way valve in heat position

  5. #5
    Join Date
    Nov 2012
    Location
    EYGPT.DAMITTA
    Posts
    37
    Rep Power
    0

    Re: Problems in thermo king sl 200

    3 way valve and solned is good

  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Problems in thermo king sl 200

    What happens if you take wires off solenoid and start the engine does the suction pressure drop it sounds like it's in heat mode to me or the 3way valve is in the heat position.

  7. #7
    Join Date
    Nov 2012
    Location
    EYGPT.DAMITTA
    Posts
    37
    Rep Power
    0

    Re: Problems in thermo king sl 200

    Are there any other suggestions

  8. #8
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Problems in thermo king sl 200

    Not familiar with the SL units.
    What's your suction pressure under the throttling valve?
    Is the suction line frosting?
    What was the original complaint?
    Did you get a solid 500 micron vaccuum?
    What's your ambient? 300 high side might not be out of line in high ambient and a sketchy condenser.
    I'd start with doing a combined heat test, but it may not be helpful with only half charge.

  9. #9
    Join Date
    Nov 2012
    Location
    EYGPT.DAMITTA
    Posts
    37
    Rep Power
    0

    Re: Problems in thermo king sl 200

    Cooling slow
    pressure under the throttling valve is 20
    pressure up the throttling valve is 160
    High pressure 300
    Knowing that the amount of gas is incomplete
    It takes 3 hours from 29 degrees to 0 degrees and empty Fund

  10. #10
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    347
    Rep Power
    18

    Re: Problems in thermo king sl 200

    your suction under the throttling valve is supposed to be 28psi, that would explain slow cooling.
    From +29 to 0 in three hours with a hot empty box isn't too bad.
    Adjust the throttling valve to 28psi by adding more shims.
    Get on the roof with a pressure washer (unit off) and clean the condenser to get the head pressure down a bit.
    300 psi head is OK for the ambient. Complete the charge. The throttling valve will protect the compressor. The unit will run at 420psi no worries.