14-08-2015, 06:58 PM #1
ariagel chiller
Hey has any one ever had any rub ins with this chiller. I have a chiller that keeps going out on antifreeze but I don't know why. I have adjusted the set point to 12degrees and it hasnt done it since but i this isnt solving the problem as its still there if i lower the set point to 10 degrees. Ics have sent me.manuals god knows how they got hold of them becauae they said they have never heard of them. They was part of delonghi who are now climaventa they still dont know. Any one know who stocks these parts as well. Thanks in advanced
-
15-08-2015, 08:57 AM #2
Re: ariagel chiller
Sounds like low water flow rate as antifreeze is usually 4c check strainer also is it tripping on controller antifreeze setting or an antifreeze stat.
-
15-08-2015, 04:02 PM #3
Re: ariagel chiller
Have you checked the actual fluid temperature at the alarm point?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
15-08-2015, 04:50 PM #4
Re: ariagel chiller
The water was 23 degrees and it takes over half hour to come down to 11.4 degrees. Pumps are fine and the strainer is clean too. Who actually makes these chillers because we have 4 on a new site and they are serving critical areas but know one knows where to get spares
-
15-08-2015, 10:42 PM #5
Re: ariagel chiller
Found an Italian company that lists Ariagel, might be worth a try.
http://www.ricambiclima.it/default.asp?locale=enBrian - Newton Abbot, Devon, UK