    toshiba wall mounted split



    hi all
    got a problem with a toshiba split indoor RAS13SHHP-ES outdoor RAS13S2AH-ES
    First visit found indoor leds flashing which my mate looked up and said it was a faulty compressor
    sure enough the compressor was red hot so we left it a day to cool.next day we looked again and
    you could hear compressor hum but would not run,so we changed the compressor,start relay and
    capacitor.
    this time when you switch on the indoor fan runs normaly,but as soon as it switches the compressor the leds flash again realy quickly.there is a 240v output from the indoor unit to the outdoor unit but only for about 4 seconds then the lights flash again.tried disconnecting compressor and condenser fan, but same thing happens.beginning to think it must be an indoor pcboard problem as there is no board on the outdoor.
    has anyone had this fault and could help.
    thanks doorswing



  2. #2
    Join Date
    Feb 2013
    Location
    Romania
    Age
    40
    Posts
    2
    Rep Power
    0

    Re: toshiba wall mounted split

    Did you replace the compressor with a new one or with an used one?
    Did you check the resistances of the winding's of the new compressor against each other and also against the ground?
    If the pcb is delivering 240v between 1&2 it is working normally.. i think..

  3. #3
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: toshiba wall mounted split

    hi nick
    fitted new compressor,found resistance of windings balanced at 4-5ohm,and checked down to earth,all ok voltage at 240v is there for a few seconds at 1&2 but as soon as it switches leds flash like the old fruit machines.