    Digital scroll condensing unit



    Hi
    I have to look at this unit tommorrow any advice greatly appreciated
    fault is its running 5 indoor refrigerated cabinets but 1 unit fluctuates in temp from 3c up to 20
    another engineer reported that it only comes down to temp when the unit next to it cuts out and requires no cooling ?
    Any thoughts I have not done much on these before any heads up or thoughts would be great
    thanks



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Digital scroll condensing unit

    Lack of refrigerant? Leak?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Digital scroll condensing unit

    Undersized condensing unit?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Digital scroll condensing unit

    Hi Sean
    Often these units have never been properly commissioned as to save money they are often installed by split bashers with little fridge system knowledge. the digital scroll has an unloader head which controls the systems suction pressure . The controller is set up to control the systems suction pressure by unloading the compressor, this allows the condensing unit to operate at reduced capacity when one or more of the cabinets are satisfied. So the suction set point in the controller needs to be checked against the requirements of the cabinets ie the suction needs to be approx. 8Deg C below the lowest cabinet set point temperature.
    The cabinets also need checking as many of these cabinets use electronic expansion valves and often the control sensors for the superheat control are in the wrong position on the evaporator, and may need moving to a better position. If there TEVs checked their superheat setting and adjust as required