    York chiller YAEP Micro Control system program - Reprogram type of refrigerant to run



    Hi,
    I have the following problem. Kindly advise if anybody has expertize about the york systems.

    Initially there was a power fluctuation, display went off, unit not running, try to reset but no use.
    a) replaced the power board and display unit - problem not solved
    b) replaced processor board with old eprom -same
    c) revert the old board but replaced the battery from new board, keep the power ON for some hours.

    Got the display back...but

    I find factory settings require reprogramming. "Reprogram type of refrigerant to run"
    when I try to enter through Keypad- 22 for R22, there is no response.

    How I can reprogram the factory settings and what is the code for program?
    controller - YAEP Micro based control system
    unit - YAEP99WD9C50PA, China

    pl suggest, thanks in advance.



  2. #2
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: York chiller YAEP Micro Control system program - Reprogram type of refrigerant to

    i dont know of any codes but if it works like a trend controller once the battery is dead,the controller loses all data and you need a laptop to download the program into the controller again.if you are carefull and change the
    battery while the power is on it saves the data.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: York chiller YAEP Micro Control system program - Reprogram type of refrigerant to

    In a low battery condition, the MANUAL OVERRIDE key
    will zero out the daily schedule to allow unlimited
    operation regardless of the time on the internal clock.
    Default values will also be loaded into memory for all
    setpoints and cutouts. These may require
    reprogramming to assure they meet chiller operating
    requirements. In addition, the low battery message
    which is displayed for this condition will disappear.
    If a power failure should again occur, the
    above process will again need to be repeated
    to bring the chiller back on line.
    In the unlikely event the low battery message should
    ever appear, it will require the RTC Chip U13 on the
    Microprocessor Board (Refer to Logic Section) to be
    replaced.

  4. #4
    Join Date
    Dec 2008
    Location
    UNITED ARAB EMIRATES
    Posts
    49
    Rep Power
    0

    Re: York chiller YAEP Micro Control system program - Reprogram type of refrigerant to

    Hi travo

    i faced this problem before, now you programe and then put password 7296 or 7396 then you can change the refrigerant

  5. #5
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: York chiller YAEP Micro Control system program - Reprogram type of refrigerant to

    Yes Mr. Qasim, I totally agree with you. Use the given password and then reprogram the other parameters.
    Quote Originally Posted by qasim2906 View Post
    Hi travo

    i faced this problem before, now you programe and then put password 7296 or 7396 then you can change the refrigerant