    Hi All

    I have a small leak on a vrf system.
    All the units are above the ceiling in a occupied very busy office.
    I charged the system with 10 Bar Trace a gas and gone around with a suitable leak detector but no finds so far.
    So I was thinking of upping the pressure for r410a
    Say 35 bar to try and help locate the leak.
    I'm not sure if this is true but I've been told under the pressure regulations I can only pressurise too 10 bar and not above with customers present
    Is this True ?
    Will it need to be done out of hours ?
    Have really dealt with the pressure regulations before ?

    Thanks Ian



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Toshiba Vrf Pressure Testing

    Not 100% up on the regs either but..... You are leak testing and not strength testing remember.

    I would agree that 10 bar is not a suitable pressure for leak testing, up the pressure in 5 bar steps until you start losing pressure then test at that pressure.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba Vrf Pressure Testing

    if you've got a tiny leak, banging nitro in to 40 bar or 41 bar to be precise- there is no risk to the staff- you could shut the service valves to test just the condenser first- usually its on the schraeders , valve caps or the condenser coil, then maybe pressurise the pipework in increments of 5 bar at a time (gives you piece of mind)

  4. #4
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17
    Hi lads

    Cheers I always done it like that in the past.
    But with health and safety and blame culture etc i was concerned with what I was told.
    So just wanted to put it out there.
    And see what you lot thought and just check I was carrying out the standard correct procedures.
    If anyone has any pdf etc Ior guides on pressure testing etc would be helpful and appreciated.

    Thanks Again

    Kind Regards Ian

  5. #5
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Toshiba Vrf Pressure Testing

    Put pressure in all tubes together. EEV in close position, you can kill them.

  6. #6
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17
    Cheers

    I did manage too put the system and indoor units into recovery mode

    Still can't find a Leak ahhhhhhhh

    Leaving it on 40 bar over the weekend

    Ian

  7. #7
    Join Date
    Jan 2008
    Location
    UK
    Posts
    20
    Rep Power
    0

    Re: Toshiba Vrf Pressure Testing

    Recently found leak on Super Heat Recovery Unit visually by seeing dirt sticking to front left condenser where copper enters/leaves metal end plates, vibration or expansion contraction? I isolated faulty section of condenser.
    Also had badly made flare on BS box which only leaked in heating mode.

  8. #8
    Join Date
    Mar 2008
    Location
    u.k
    Posts
    62
    Rep Power
    17
    Thanks mate

    Still looking uv dye added now
    And return checks 64m of pipe work 9 indoor units a nightmare
    Looking too replace the kit now

    Ian