    Vacuum.



    I've been pulling a vacuum on a big VRV system which has been retrofitted . We reclaimed all the old R410 and fitted new indoor and outdoor units using existing pipe work. All Bs boxes and indoor units have flare fittings. I have been trying to pull a vacuum and am not sure if I've got a leak because I can't get it down past 20000micron. I've had the pump on for 8 hours. Because of all the oil polyester oil in the pipes could I be battling to get the vacuum? Or do I have a leak. It held 400 pasig for 12 hours.( nitrogen).


    The more I learn the less I know......

  2. #2
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Vacuum.

    Hi Drew
    Could be a few things.
    1) POE is highly hydroscopic (absorbs water) so how long was the system open to atmosphere as moisture ingress can be very quick, with POE.
    2) IS the vac pump big enough
    3) Have you changed the vac pump oil ?.
    4) The pressure test sounds good, so try breaking the vacuum with nitrogen, and re vacing the system to see if any improvement.
    5) Energise the compressor heaters and any other heaters on the system to help remove any moisture during the vac
    6) Try another vac guage to double check

    If no improvement its back to re gas testing
    Best of luck

  3. #3
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Vacuum.

    Have you removed the shraeder valve cores from the service valves as this makes a big difference - recently on a new install left a vac pump on all weekend, couldn't pull a decent vac, so removed the shraeders, 12 house later bingo, 0.5 torr...

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Vacuum.

    Quote Originally Posted by Glenn Moore View Post
    Hi Drew
    Could be a few things.
    1) POE is highly hydroscopic (absorbs water) so how long was the system open to atmosphere as moisture ingress can be very quick, with POE.
    2) IS the vac pump big enough
    3) Have you changed the vac pump oil ?.
    4) The pressure test sounds good, so try breaking the vacuum with nitrogen, and re vacing the system to see if any improvement.
    5) Energise the compressor heaters and any other heaters on the system to help remove any moisture during the vac
    6) Try another vac guage to double check

    If no improvement its back to re gas testing
    Best of luck
    glenn, you are correct, i have same experience before,after replacing vac pump oil reached to 500 micron.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Vacuum.

    Quote Originally Posted by CONROD View Post
    Have you removed the shraeder valve cores from the service valves as this makes a big difference - recently on a new install left a vac pump on all weekend, couldn't pull a decent vac, so removed the shraeders, 12 house later bingo, 0.5 torr...
    Basic advice, but highly relevant all the same.
    But Not for Drew methinks!
    Sadly some joints can be gas tight at Positive Pressure, but leak under negative pressure.
    An interesting post Drew.
    Thanks Grizzly


    Grizzly
    Last edited by Grizzly; 15-07-2015 at 06:43 AM.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Vacuum.

    Try a vacuum rise test, maybe isolate outdoor units and just vac pipework and indoors, used compressor oil can be a pain to vac due to the refrigerant dissolved in it but 20,000 sounds a high vacuum to get stuck on.

    Is the vac gauge accurate?
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: Vacuum.

    Thanks for the replies guys.
    We re pressurised the system and found a leaky flare. Confusion with regard why it held pressure previously? Their has been talk about us not have driven all the bs boxes open correctly. I am easily confused when I have to push certain buttons in sequence and might have only pushed the set button 20 times instead of 21? It held pressure and pulled a decent vacuum after repairing the flare.
    these VRV systems will be the end of me. I feel sorry for the apprentices coming through having to face these. I hardly recognise anything in the outdoor units anymore.
    thanks again.
    Last edited by Drew; 22-07-2015 at 09:06 AM.
    The more I learn the less I know......

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Vacuum.

    Add on of these to your tool box and kiss leaky flare nuts goodbye.