    Daikin question???



    Hi was woundering if anyone can help me with an issue I have with some vrv units.
    Have 4 ducted indoor units off 1 BRC1D controler. The controler says unit 4 is AF. I know the fault is about the float switch. But is there a way to figure out which indoor is unit no 4 from the controler? Could save me a lot of pain trying to gain access to units that are not in fault. Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin question???

    Turn the units off.

    Now use the settings code to run the individual unit fans one by one. . You can then identify which unit is which.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin question???

    pull each drain plug to see which indoor had the most water

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin question???

    The AF fault shoud stop the unit so just look for the 1 without the fan running

  5. #5
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: Daikin question???

    As frank said. Also I think if you put it in code 43 it will run the indoor fan and you use the diamond button to go through the units. I haven't done this for a long time so might be wrong

  6. #6
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Daikin question???

    I think the unit will hit high level. A few times be fore it. Sends out a fault.
    any problems. With the drains or the trap? Just a thought .

  7. #7
    Join Date
    Feb 2010
    Location
    Ireland
    Age
    38
    Posts
    82
    Rep Power
    15

    Re: Daikin question???

    Went to site last nite to investigate fault. Trick with the forced fan worked great. Took unit apart and found a lot of sludge in the drip tray. Washed out all the crap and tested the pump all seems good now unit lifted water away out of the drip tray and down the drain. Hopefully that's all it was. Thanks for the help everyone hope to be able to help others on here if I can.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin question???

    Glad we could help and that you've sorted the problem.
    Brian - Newton Abbot, Devon, UK