Results 1 to 9 of 9
    Feb 2007
    YORKSHIRE
    Discharge superheat
    Hi guys can you confirm this is correct as I am doubting myself
    discharge superheat
    1 x discharge pressure & check with comparator what temperature it is
    2 x measure actual discharge temp
    3 x difference between 2 give s you discharge superheat
    r407c chiller @ 100%
    discharge pressure 16.5 bar = 40C
    discharge temp 64C
    discharge superheat 24C ??????
    is this correct
    cheers guys
    3,355
    Re: Discharge superheat
    Yes you are correct
    Feb 2007
    YORKSHIRE
    Thanks mate
    superheat & sub cooling I am ok but was doubting myself with dsh
    is a 20C diff normal
    high discharge superheat short of gas ?
    low discharge superheat over charged ?
    3,355
    Each type of refrigerant is different as to discharge temperature.
    20 deg sounds ok to me but have you checked suction superheat at evaporator?
    If it was a screw you need minimum 15 deg C to drive refrigerant out of oil for good lubrication.
    Feb 2007
    YORKSHIRE
    Superheat 6C & sub cooling 9C
    chiller operating fine just was not sure about discharge superheat
    thanks again
    3,355
    To me it's fine, as superheat perfect, not much else you can do.
    What type of compressor is it.
    Feb 2007
    YORKSHIRE
    Hitachi screws mate
    3,355
    Quote Originally Posted by stevo4546 View Post
    Hitachi screws mate
    No no problem then
    3,355
    Forgot to ask oil temperature of screw & how it is cooled, as that can also influence discharge temperature (although yours still sounds ok)
    oil il temp should be approx 15 deg C higher than SDT & discharge temp a bit higher than oil temp.