    I think the Cooler Drain line is Blocked!



    Hi Guys.

    Check out the attached Photo, May I add the Blanking plate hanging of the end is Stainless Steel.

    Which originally sat behind It's Locking Ring pictured on the end of the pipe. That's a 65mm diameter pipe by the Way!

    It just shows the raw power of expanding Ice.

    Attachment 13804

    Grizzly



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: I think the Cooler Drain line is Blocked!

    RJT fitting? That would take some pressure to deform!
    Mostly found in Oxfordshire, UK :)

  3. #3
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: I think the Cooler Drain line is Blocked!

    From the phase change diagram you are probably looking at around 2 K Bar of pressure at -20 Deg C
    or over 100 MPa

    An RJT fitting is rated to 25 Bar, poor thing did not stand a chance!
    I love the smell of Ammonia in the morning!