    carrier 30gx chiller EXV problem



    Dear all.
    we have a carrier 30gx chiller its expansion valve is not opening,we try through test its opening .but in normal condition its not working please help me to fix this



  2. #2
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: carrier 30gx chiller EXV problem

    Have you checked if the low pressure transducer and superheat probe is showing correct values?

  3. #3
    Join Date
    May 2008
    Location
    uae
    Age
    44
    Posts
    40
    Rep Power
    0

    Re: carrier 30gx chiller EXV problem

    suction pressure and superheat are showing actual values

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: carrier 30gx chiller EXV problem


  5. #5
    Join Date
    Oct 2009
    Location
    Norway
    Posts
    39
    Rep Power
    0

    Re: carrier 30gx chiller EXV problem

    How did you test the exv?
    the water inlet/outlet probes are also showing correct values?
    Is there a seperate fuse for the exv?
    Have you checked the sub menu that the exv is requesting opening and measured the signal given to the exv?