    Nov 2008
    nepal
    125
    Mitsubishi VRF indoor units not cooling suffeciently
    hi friends, i have installed Mitsubishi VRF but indoor units are not cooling sufficiently,
    could any body help me to figure out the problem.on the remote controller there is no error shown, phase on the indoor is also ok.below are the model no of IDU and ODU.
    Model no of ODU:PUHY-P450YHA(-BS)
    Model no of IDU: PEFY-P250VMH-E x 2 Nos
    Aug 2009
    Dartford
    88
    Re: Mitsubishi VRF indoor units not cooling suffeciently
    Have you checked the refrigerant charge? What pressures are you getting? What temperatures?
    Nov 2008
    nepal
    125
    @Deano240: yes i have added the refrigerant charge. i am getting only 18 Ampere on cooling mode and on this Amps : high pressure = 450 and low pressure =115.but after few minutes it comes to 15 Ampere and on this Amps: high pressure = 350 and low pressure = 110.now its running on 12/13 Amps.hope this data works.
    manchester
    5,639
    are u clipping the comp current on the leads or the incoming power to the outdoor?, did you pressure test with ofn (nitrogen) prior to powering up?
    was nitrogen used to purge whilst brazing?
    use the dipswitches on the outdoor sw1 to read compressor freq, maybe set sw1,1 on indoor (address pcb) to use the thermistor in the remote controller instead of the return air thermistor. (if its in the conditioned space)
    Feb 2015
    uk
    whats your air off the cassettes it should normally be between around 10oc
    Feb 2015
    uk
    and what refrigerant do they run off
    Nov 2008
    nepal
    125
    Dear Install monkey: yes i have tested the pressure with Nitrogen.but what i did yesterday, i just turn off all dipswithch off of SW1 and its working fine.