    Mitsubishi VRF indoor units not cooling suffeciently



    hi friends, i have installed Mitsubishi VRF but indoor units are not cooling sufficiently,
    could any body help me to figure out the problem.on the remote controller there is no error shown, phase on the indoor is also ok.below are the model no of IDU and ODU.

    Model no of ODU:PUHY-P450YHA(-BS)

    Model no of IDU: PEFY-P250VMH-E x 2 Nos



  2. #2
    Join Date
    Aug 2009
    Location
    Dartford
    Age
    34
    Posts
    88
    Rep Power
    15

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    Have you checked the refrigerant charge? What pressures are you getting? What temperatures?

  3. #3
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    @Deano240: yes i have added the refrigerant charge. i am getting only 18 Ampere on cooling mode and on this Amps : high pressure = 450 and low pressure =115.but after few minutes it comes to 15 Ampere and on this Amps: high pressure = 350 and low pressure = 110.now its running on 12/13 Amps.hope this data works.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    are u clipping the comp current on the leads or the incoming power to the outdoor?, did you pressure test with ofn (nitrogen) prior to powering up?
    was nitrogen used to purge whilst brazing?
    use the dipswitches on the outdoor sw1 to read compressor freq, maybe set sw1,1 on indoor (address pcb) to use the thermistor in the remote controller instead of the return air thermistor. (if its in the conditioned space)

  5. #5
    Join Date
    Feb 2015
    Location
    uk
    Posts
    36
    Rep Power
    0

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    whats your air off the cassettes it should normally be between around 10oc

  6. #6
    Join Date
    Feb 2015
    Location
    uk
    Posts
    36
    Rep Power
    0

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    and what refrigerant do they run off

  7. #7
    Join Date
    Nov 2008
    Location
    nepal
    Posts
    125
    Rep Power
    16

    Re: Mitsubishi VRF indoor units not cooling suffeciently

    Quote Originally Posted by install monkey View Post
    are u clipping the comp current on the leads or the incoming power to the outdoor?, did you pressure test with ofn (nitrogen) prior to powering up?
    was nitrogen used to purge whilst brazing?
    use the dipswitches on the outdoor sw1 to read compressor freq, maybe set sw1,1 on indoor (address pcb) to use the thermistor in the remote controller instead of the return air thermistor. (if its in the conditioned space)
    Dear Install monkey: yes i have tested the pressure with Nitrogen.but what i did yesterday, i just turn off all dipswithch off of SW1 and its working fine.