    Serious problem with Chiller Carrier 23XRV



    Dear all,
    - Fault state is 220: Ground Fault Trip; Check Motor and Current Sensors
    - 2 minutes later, error appears 223 :Ground Fault Trip; Check Motor and Current Sensors
    I checked GROUND FAULT CURRENT andVFD FAULT CODE in VFD_HIST screen , the fault code is 216.
    When this error appear, I can't reset on ICVC display. I have to off power supply to Chiller, error reset
    I measured grounded input wiring and insulation cable is OK
    This is the 3rd time I encountered this error.
    Can you give me any advice?
    Best regards!
    Thank you so much!



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Serious problem with Chiller Carrier 23XRV

    Hi
    check your cabling ,since you are using a vsd,the cabling must be low capacitance shielded cabling .

    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Sep 2008
    Location
    Viet Nam
    Age
    39
    Posts
    4
    Rep Power
    0

    Re: Serious problem with Chiller Carrier 23XRV

    Quote Originally Posted by goshen View Post
    Hi
    check your cabling ,since you are using a vsd,the cabling must be low capacitance shielded cabling .

    good luck
    Thank for your answer!
    I used megaohm check cabling. I stiil not see anything unusual,
    Best regard!