    DX Coil Control



    Hell there, I have been asked to connect a Toshiba RAV-SM564ATP-E condenser unit to a DX coil mounted in a AHU. Am I right to assume that as the expansion device is in the condenser unit I need no further control at the coil?
    Pipe sizes are 1/4" and 1/2"
    The condenser is the same type you would fit on a split a/c system.
    Many thanks in advance for any advice on this



  2. #2
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    87
    Rep Power
    13

    Re: DX Coil Control

    Hi Tony, I have worked on similar equipment and I was instructed to install TXV at the coil as this is where the change in state is happening and so where the flow needs to be monitored and controlled.
    Martin

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: DX Coil Control

    No TXV needed, Toshiba should have provided an AHU interface kit with temperature sensors, these are fitted on the evap coil and connect to the interface.
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    May 2008
    Location
    CROYDON
    Age
    61
    Posts
    13
    Rep Power
    0

    Re: DX Coil Control

    Thanks guys Al your right managed to get some more paperwork on this project and your right, sensors and interface kit provided..