Thread: Lennox LCH 803
-
20-06-2015, 02:51 PM #1
Lennox LCH 803
Hello all
chiller Lennox LCH803
How to disable the operation of the compressor 1,2
Controller CLIMATIC 50
In the work leave the compressor 3
Thank you for your support
-
20-06-2015, 06:58 PM #2
Surely they have there own breakers?
Martin
-
20-06-2015, 07:11 PM #3
Re: Lennox LCH 803
disable by modifying the parameters of the program
-
20-06-2015, 07:50 PM #4
Do you mind if I ask why?
See free contacts;
image-3573839729.jpgMartin
-
21-06-2015, 09:57 AM #5
Re: Lennox LCH 803
Martin
Thank you for contact (free) information
-
21-06-2015, 12:14 PM #6
Re: Lennox LCH 803
Hi *****959.
Following on from Martin's post.
I cannot confirm these settings will work with your 3 compressor model LCH.
But 3411 is for comp 1 and 3412 is for comp 2 on some models. Once entered you should be able to switch the relevant comp on or off!
Grizzly
-
21-06-2015, 01:57 PM #7
Re: Lennox LCH 803
Hi Grizzly
it's clear
Setting(code 3000)>1.General
2.Schedule
3.Control
4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Rotat.(cod3410)>3411
>3412
Thank you
-
21-06-2015, 02:00 PM #8
Re: Lennox LCH 803
correction
1 Rotat.>3411
>3412
Thank you
-
24-06-2015, 06:01 PM #9
Re: Lennox LCH 803
Hi Grizzly
right
4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Enable.(cod3411)
choose from ready-made
С1--
С-2-
С1.2-
С--3
С1-3
С-2.3
С1.2.3. Thank you