Results 1 to 9 of 9
Thread: Lennox LCH 803
    May 2014
    Moskow
    56
    22
    Lennox LCH 803
    Hello all
    chiller Lennox LCH803
    How to disable the operation of the compressor 1,2
    Controller CLIMATIC 50
    In the work leave the compressor 3
    Thank you for your support
    Aug 2013
    Hampshire
    32
    93
    7
    Surely they have there own breakers?
    Martin
    May 2014
    Moskow
    56
    22
    Re: Lennox LCH 803
    disable by modifying the parameters of the program
    Aug 2013
    Hampshire
    32
    93
    7
    Do you mind if I ask why?
    See free contacts;
    Martin
    May 2014
    Moskow
    56
    22
    Re: Lennox LCH 803
    Martin
    Thank you for contact (free) information
    Somerset
    63
    4,529
    38
    Re: Lennox LCH 803
    Hi *****959.
    Following on from Martin's post.
    I cannot confirm these settings will work with your 3 compressor model LCH.
    But 3411 is for comp 1 and 3412 is for comp 2 on some models. Once entered you should be able to switch the relevant comp on or off!
    May 2014
    Moskow
    56
    22
    Re: Lennox LCH 803
    Hi Grizzly
    it's clear
    Setting(code 3000)>1.General
    2.Schedule
    3.Control
    4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Rotat.(cod3410)>3411
    >3412
    Thank you
    May 2014
    Moskow
    56
    22
    Re: Lennox LCH 803
    correction
    1 Rotat.>3411
    >3412
    Thank you
    May 2014
    Moskow
    56
    22
    Re: Lennox LCH 803
    Hi Grizzly
    right
    4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Enable.(cod3411)
    choose from ready-made
    С1--
    С-2-
    С1.2-
    С--3
    С1-3
    С-2.3
    С1.2.3. Thank you