    Tk ts 200



    got a code 68 up internal controller ? Any assistance gents never had this one before ta charlie



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Tk ts 200

    Connect to pc do a cold start if it comes back change the micro.

  3. #3
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Tk ts 200

    Quote Originally Posted by cadwaladr View Post
    Connect to pc do a cold start if it comes back change the micro.
    TS-200 will be a uP-T so you'll need to do a cold start via jumper J200.

  4. #4
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Tk ts 200

    Thanks for input gents .....plugged it in and had eractic voltage only when they where loading unloading trailer and found some freak of nature had wired some interior lights straight to the fridge and yes u guessed it no fuses anyway one light full of water and they had wired it to the run circuit so cut it out and ain't missed a beat yet