    Daikin pcb



    Can anyone help we have 2 ftxs 25 wall mounted units on a multi of 2mxs 50 only 6 months old a board was faulty on one indoor unit we change the board over and we are getting a code of u4 which is comication but now we have a problem the other unit does not work now we reset the power
    This is strange



  2. #2
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    93
    Rep Power
    13
    This is the most common fault code when installing new kit, something is wired incorrectly. As the two indoor units will be linked together, if something was wired wrong when changing the pcb you may have damaged the pcb in the other unit. Double check all the wiring and continuity between the two units.

    I have seen poorly connected cables in crimps between linked units that have come loose when fiddling with the system and moving pipes/cables so check for that too. Wall mounted units are notoriously simple so the problem should be easy to find.
    Martin

  3. #3
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin pcb

    Hi this was working great for two months all new pipes and cables Pipe and cable run 9 m at the most when installed each unit was check on its on so we must be something simple

  4. #4
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    93
    Rep Power
    13

    Re: Daikin pcb

    Maybe the wrong board was fitted? Is the unit with the new board the master? Have you tried running each on there own since changing the board? That will tell you if it is a comms problem between the two or from outside to in or if the other unit is at fault
    Martin

  5. #5
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    187
    Rep Power
    19

    Re: Daikin pcb

    Do you have a isolator. For each indoor unit?
    and switched your comms cable?
    check colours on your 1,2,3 indoor to outdoor.
    sadly checking things by swapping boards can be expensive.
    good luck.

  6. #6
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin pcb

    Thanks all will try

  7. #7
    Join Date
    Jan 2013
    Location
    portugal
    Age
    38
    Posts
    2
    Rep Power
    0

    Re: Daikin pcb

    If it says communication error check and clean each connector pins. There might be a loose connection. I am not sure if your unit can perform test for the input sensors, if it can check all input sensors.

    Regards,
    Toprak S.
    Last edited by frank; 30-06-2015 at 07:50 PM.

  8. #8
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    53
    Posts
    207
    Rep Power
    17

    Re: Daikin pcb

    Thanks tried all that no luck