    not pumping down



    Looking at a cold store today customer said it not stopping when door switch activated the switch is a basic switch that could be used for lighting etc,this switch energizes the liquid line mag valve,checked no power at valve attached gauges suction pressure high 65psi closed receiver valve ,no difference closed suction valve no difference? Asked customer if temperature log shows any warm readings no all seems to be right the compressor is a maneurop mtz 64 back to the compressor again closed valves again all works fine? I suspect the compressor is faulty as the customer said it did not stop when entry switch was used yesterday,any ideas has this happened to anyone in the past



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: not pumping down

    defective discharge or suction valves on the compressor?
    works one minute, doesn't work the next, sounds like something is wobbling around inside the compressor.
    -Cheers-

    Tycho

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: not pumping down

    That's my guess looks like order a replacement

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: not pumping down

    Is it a scroll? Not sure if these will run backwards.

    Had Copeland scrolls where the trip on LP but the the LP resets as the compressor is spinning backwards and it keeps running that way, runs like it till goes out on klixon then runs ok when resets.
    Last edited by chemi-cool; 16-06-2015 at 08:31 PM.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: not pumping down

    Quote Originally Posted by monkey spanners View Post
    Is it a scroll? Not sure if these will run backwards.

    Had Copeland scrolls where the trip on LP but the the LP resets as the compressor is spinning backwards and it keeps running that way, runs like it till goes out on klixon then runs ok when resets.
    John, MTZ is recip.

    Most probably valves are broken inside the compressor.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: not pumping down

    Quote Originally Posted by chemi-cool View Post
    John, MTZ is recip.

    Most probably valves are broken inside the compressor.
    Thanks Chemi, Aha! Don't see many maneurops, they are one of the more expensive makes here.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Feb 2015
    Location
    uk
    Posts
    36
    Rep Power
    0

    Re: not pumping down

    i had 3 phase pots run backwards on a big trane unit unit because the phases were switched by sparkies , it was my first month on the tools by myself , i had no idea what was going on except the pots seemed to be spinning backwards , i was pulling my hair out for a good few hours and had to ring the boss to come and help me , the joys of being new to the job

  8. #8
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: not pumping down

    This compressor must be working ok now,as I have had no call from the customer.

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: not pumping down

    .

    I think the Maneurops have a pressure relief valve inside
    the comp to prevent over pressurization?

    If this is the case it is possible it activated and now has
    sorted itself out?

    If it is now OK and if it is running, then leave it alone.
    I might last a week, a month or another year. Whatever
    it does if it is OK take all the credit.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  10. #10
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: not pumping down

    You could be right Rob,anyway if not broke why fix it.