    Buffer tank



    Hi all,
    I want to design a chilled water buffer tank most of the books refer to vertical tanks but I'm looking for horizontal tank al tanks,can anyone give some technical documents of the same..books,websites anything ........



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Buffer tank

    The design of vertical buffer tank is usually related to space saving.
    I don't see any reason why you can't design an horizontal one.

    I would suggest you to design it round one and place it in a small [2%] slope towards the outlet valve to keep it clean.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Buffer tank

    Hi
    generally buffer storage vessels are designed to give average 15% chilled water capacity volume expressed as a thermal storage volume. Bare in mind the floor loadings if at top of a building, then include baffles for water surge effect as well. Generally cross flow for maximizing regeneration to heat source.
    There are formulas in " engineering tool box " google it. Vertical or horizontal earth quakes can be damaging with large volume vessels.
    magoo