    rotary to reciprocating compressor and vice versa



    Hi
    from hot zone in temperature and wars
    temperatur these days reached 47 c and may exceed it
    my question about ac split unit
    non inverter
    is there any problem if you replace the reciprocating compressor to rotary
    or vice versa
    whatr are the advantages and disdvantages


    Power consists not in being able to strike another but in being able to control oneself when anger arises

  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: rotary to reciprocating compressor and vice versa

    I think rotary compressors work work better in heating mode than reciprocating ones (more heat goes into the room), plus they are quieter, but i don't know of any problems with swapping from one type to the other so long as the duty is similar and refrigerant type similar.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: rotary to reciprocating compressor and vice versa

    .

    I agree with the Monkey, there will be no operational problems
    as long as the two are the same duty, but I don't know of many
    AC systems that use reciprocating comps because of the noise issues
    of the gas pulsing through the system.

    Most AC's are either rotor or scroll in design.

    Regards

    Rob.

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: rotary to reciprocating compressor and vice versa

    the cause behind replacing reciprocating compressor( which is more powerful than rotary) to rotarty
    is unstable supplied ac voltaage in iraq
    the supplied voltage must be 220 -240
    but in most area the supllied voltage is 190-180 or lower
    so recprocating compressor can withstand the decrease in voltage to 195 volt
    while rotary can handle to 182 volt
    Power consists not in being able to strike another but in being able to control oneself when anger arises

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: rotary to reciprocating compressor and vice versa

    I would not say so! But some manufacturers have compressor models which can start with greater voltage drop than others.
    Such example is Fujitsu General which is made in India. They are capable to start with greater voltage drop than Fujitsu without "General" in its name!
    Therefore, I suggest you to find some India made compressors, since they are more suitable for greater voltage drop at starting.