    Good morning , someone can help me with the wire connections to the UNISAB III Controller?
    X10,X11, X12.......
    It would be great to have access to electrical drawings.
    thank you very much.
  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32
    Re: UNISAB III Connections
    Hi Jose
    X10 block is your digital outputs
    X11 is communications RS485
    X12 block is digital outputs for externals i.e.alarms shutdowns etc.
    X13 safeties
    Not sure exactly what your request is for? Are you upgrading, fault finding or just for knowledge