Hi can any one help we install a brand new Ac system with 1 ftxs 42 2 ftxs 20 and a ftxs 25
cools perfect for 6 hours after that the indoors green lights start to flash any one can help on this
-
07-06-2015, 11:00 PM #2
Re: Daikin Mxs 68
Press and hold the cancel button on the controller. Then keep pressing it until u hear a continous beep. What ever displays on th controller is the fault code.
Hope this helps
-
12-06-2015, 05:56 PM #3
Re: Daikin Mxs 68
How did you get on with your fault?
all pipes and wiring going to correct units?
how much pipe have you got in total?
i could be wrong , but the total size of your indoor units exceed the size of your out door unit.
outdoor 68.
indoor total 87.
-
16-06-2015, 06:58 AM #4
Re: Daikin Mxs 68
Hi
the wires were crossed thanks for your help