    Unhappy Phantom leak help needed



    System tested at 10 bar for 30 minutes each part
    System break down as fallows
    1. Compressor discharge to receiver out let
    2. Receiver to cabinet before TEV
    3. TEV to cabinet suction out
    4. Suction line
    Each section has isolation valves all were closed and started with rest Line connected to compressor for 30 minutes then tev iso valve and last suction out to condensing unit but no drop?
    But system looses gas



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Phantom leak help needed

    Hi it might leak when the joints get hot, or at higher pressure,

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Phantom leak help needed

    Is this a commercial cabinet? Sometimes putting a little refrigerant in the system pressurised with nitrogen get the sniffer out and check it,or throw it in a swimming pool!

  4. #4
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Phantom leak help needed

    For really difficult leaks a tracer gas is used which has a low molecule gas to pin point small holes. (Helium/Hydrogen).

    Do not to forget to check your schrader valves after removing gauge sets, many an engineer has been caught with these.
    I love the smell of Ammonia in the morning!

  5. #5
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Phantom leak help needed

    Quote Originally Posted by GHAZ View Post
    Hi it might leak when the joints get hot, or at higher pressure,
    Cant be higher pressure , heat is possiable how do i put some heat in ?

  6. #6
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Phantom leak help needed

    no schrader it has back seat service valve ( 6 hp condensing unit feeding 2x 3m dairy cabinets ) shutting down in 50 - 70 hours on lp

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Phantom leak help needed

    have you tried putting a UV dye into the system

  8. #8
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Phantom leak help needed

    Quote Originally Posted by martinw58 View Post
    have you tried putting a UV dye into the system
    yes no show in obese places

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Phantom leak help needed

    Quote Originally Posted by cryotec View Post
    Cant be higher pressure , heat is possiable how do i put some heat in ?
    10 bar is quite low for pressure testing / leak finding.

    You say it is a dairy with a 6hp comp, I can't see where
    you mention the type of refrigerant?

    If it is 404a then low side would be 32degsC = 14barg and the high side
    at 55degsC = 25barg so if you can isolate the system you can pressure
    test to higher pressures than 10barg.

    What is on the system that limits the pressure to 10barg?

    30 mins is no time either, you are wasting your time doing it this way.
    Pressure test it correctly up to it's it's safe maximum working pressure
    and then leave it for 24 hours if necessary.

    Use good quality bubbly water and check every section manually,
    if there are 2 cases isolate them and test them separately, play close attention
    to evaporator end returns.

    Does the system have a pressure release valve on the receiver?
    If it does put a party balloon on the end and see if it inflates.

    Leak testing is a systematic, boring, time consuming job but it must
    be done, leaving something for thirty mins and then putting gas into it
    is just going to result in the same way as previous attempts.

    Also don't always think it is going to be one big leak, small leaks add up.
    It could be more than one very small leak and don't forget the service
    valve. Back seating service valves are one of the most common places
    for a leak and it can be missed because we fit our gauges to them.

    Make sure you test the valve with the gauges off as well as on.

    2 x 3mtr cases lasting only 3 to 4 days then going out on LP is some doing.
    How much refrigerant? 3 or 4 Kg's in 3 days? Wow......................

    Pressurise to the highest safe limit LP switches, evaps and the LP side of the comp
    are the weak points but you could still go above 10barg (unless it was on 134a?)

    Isolate all sections and wait overnight, check inside case with bubble water and check
    all the condenser, compressor and receiver components, then start with the pipe.
    Remove section of armaflex insulation and stick a leak detector down each end.

    Check for oil, with the amount of gas loss there will be oil everywhere.

    Lastly put video cameras on it and see if someone is stealing it, you may laugh at that
    but it is becoming more and more common for people to steal refrigerants thinking
    they can get high on them (i have seen the video proof if you doubt me)


    Regards

    Rob

    .

    Rob

    .
    Last edited by Rob White; 08-06-2015 at 01:09 AM. Reason: spelling
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  10. #10
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Phantom leak help needed

    Quote Originally Posted by Rob White View Post
    10 bar is quite low for pressure testing / leak finding.

    You say it is a dairy with a 6hp comp, I can't see where
    you mention the type of refrigerant?

    If it is 404a then low side would be 32degsC = 14barg and the high side
    at 55degsC = 25barg so if you can isolate the system you can pressure
    test to higher pressures than 10barg.

    What is on the system that limits the pressure to 10barg?

    30 mins is no time either, you are wasting your time doing it this way.
    Pressure test it correctly up to it's it's safe maximum working pressure
    and then leave it for 24 hours if necessary.

    Use good quality bubbly water and check every section manually,
    if there are 2 cases isolate them and test them separately, play close attention
    to evaporator end returns.

    Does the system have a pressure release valve on the receiver?
    If it does put a party balloon on the end and see if it inflates.

    Leak testing is a systematic, boring, time consuming job but it must
    be done, leaving something for thirty mins and then putting gas into it
    is just going to result in the same way as previous attempts.

    Also don't always think it is going to be one big leak, small leaks add up.
    It could be more than one very small leak and don't forget the service
    valve. Back seating service valves are one of the most common places
    for a leak and it can be missed because we fit our gauges to them.

    Make sure you test the valve with the gauges off as well as on.

    2 x 3mtr cases lasting only 3 to 4 days then going out on LP is some doing.
    How much refrigerant? 3 or 4 Kg's in 3 days? Wow......................

    Pressurise to the highest safe limit LP switches, evaps and the LP side of the comp
    are the weak points but you could still go above 10barg (unless it was on 134a?)

    Isolate all sections and wait overnight, check inside case with bubble water and check
    all the condenser, compressor and receiver components, then start with the pipe.
    Remove section of armaflex insulation and stick a leak detector down each end.

    Check for oil, with the amount of gas loss there will be oil everywhere.

    Lastly put video cameras on it and see if someone is stealing it, you may laugh at that
    but it is becoming more and more common for people to steal refrigerants thinking
    they can get high on them (i have seen the video proof if you doubt me)


    Regards

    Rob

    .

    Rob

    .
    once again first class advice,when you pointed out what quantity is or may be being lost it certainly has one hell of a leak.

  11. #11
    Join Date
    Sep 2009
    Location
    us
    Posts
    10
    Rep Power
    0

    Re: Phantom leak help needed

    Had a small walk in freezer that had a leak that took more time to find than it should have. Pressurized to 450 psi and found the leak at the copper to brass factory connection on a solinoid valve. It seemed to leak worse while operating than with 100 psi. Maximum test pressure found it.

  12. #12
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Phantom leak help needed

    Quote Originally Posted by cadwaladr View Post
    once again first class advice,when you pointed out what quantity is or may be being lost it certainly has one hell of a leak.
    Sorry been away family matter
    Late night i could not read my writing test pressure was 20 bar and not 10 bar
    it is 404 system

  13. #13
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Phantom leak help needed

    Have you been round it with a leak detector when there,s gas in it ,make sure you check pressure switch bellows

  14. #14
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Phantom leak help needed

    Me, I would have pulled the whole system down to vacuum and then sectioned it of.

    -Vacuum system
    -Connect vacuum gauge to one of the sections
    -leave over night

    next day, observe reading on vacuum gauge

    -open one by one valve, starting with the section closest to vacuum gauge
    -observe change in vacuum between each time you open a new part of the system.

    If I know the system is loosing refrigerant and I can't find the leak with nitrogen, I always go for vacuum, and use a 0-100mbar gauge, because you get a bigger reading when you loose the vacuum than leaving the system overnight with 10 bar in it. leaving 10-20 bar in a system light leave you with the needle on the pressure gage moving 0.01 mm.

    With a 0-100 mbar gauge, you have a span of 0.1 bar, or a span of 0-1.4 psi and that's not a lot, so you can detect the tiniest of leaks
    ----------------------------------

    Also, as Rob White said, "30 mins is no time either, you are wasting your time doing it this way.
    Pressure test it correctly up to it's it's safe maximum working pressure
    and then leave it for 24 hours if necessary"

    and

    "Leak testing is a systematic, boring, time consuming job but it must
    be done, leaving something for thirty mins and then putting gas into it
    is just going to result in the same way as previous attempts."

    Both of those quotes are words to live by, it's boring as hell, but it has to be done...

    The worst part is standing around waiting, but that is a whole lot better than having to come back every 3-4 days for the same problem...
    The client will forget that you spent 15 hours trying to find the leak but fixing it, but he will never forget that you had to come back every three days for a 2 week period, making him pay for the ***** and your time, before you managed to fix it.
    -Cheers-

    Tycho

  15. #15
    Join Date
    Aug 2011
    Location
    yorkshire
    Posts
    40
    Rep Power
    0

    Re: Phantom leak help needed

    Found it !!!!!!
    32 bar no drop in 24 hours so i got sick and got a big propane torch and heated the condenser and got to about
    80 C before i saw drop
    Thanks for all your help

  16. #16
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Phantom leak help needed

    .



    Well done

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  17. #17
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Phantom leak help needed

    Wish I had been paid in full for finding leaks and faults,but nothing gives me greater pleasure in the job than sorting a system the ones that are easy compensate,an old retired fridgy mate said to me once your like a scrap yard dog you won't let go!

  18. #18
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0

    Re: Phantom leak help needed

    And the pecker head connection on the compressor, and the fuse able plug on the receiver tank.
    On split systems with long line sets, I cut and cap them with a Schrader on one end, cap and pressurize the two end pieces ( condenser and air handler ) and pump up all four, to try isolate where to look. Some are vibration leakers and dyes are usually the only way to find them.
    Last edited by hvac01453; 06-10-2015 at 02:12 AM.
    My wife says I don't listen to her....or something like that....

  19. #19
    wooleybull's Avatar
    wooleybull Guest

    Re: Phantom leak help needed

    yes if you have systematically checked all components at max test pressure u can almost guarantee its going to be in the condenser, i would be checking oil level cause there so
    should have been a **** load of oil, soaking the condenser with bubbles once you put dye in and shining you uv light on the liquid running into the condensate pan can work as well

  20. #20
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: Phantom leak help needed

    Most common leaks for me porous evap coils and receivers plugs (usually on a Friday evening)!