    HELP PLZ: Shell & Tube Selection Parameters



    Dear All,,

    Please help me out to start selection of shell and tube water cooled condensors in order to match it with refrigeration compressors, to make things systamatic and smooth for you i have some parameters am thinking about in mind:

    1- Water In/Out
    2- Heat of rejection (how can this be related to refrigeration capacity?)
    3- Condensing temp. (related to water In/Out).
    4- what is the appropriate delta T (Out-In), and what is the standard value.
    5- what is the minimum water in temp.?? is there any limitations ? ofcourse not close to zero.
    6- what is the appropriate water flow and speed for a selected condenser.

    actualy my case that i want to have 15Kw refrigeration @Tsuction -5c, which cond. temp. i shall go throw to select a compressor, and which water in temp. i have to consider, and whicg DT is applicable. in site i have from 15 to 20c water temperature to feed the condensors.

    i have noticed that all the manufacturers are stating the refrigeration capacities at 40c cond.

    i know it is too much questions, but it is the first time to use water cooled condensing units

    please your help.

    Thank you..


    Too Much Of Something Is Bad Enough

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: HELP PLZ: Shell & Tube Selection Parameters

    1) water in depends on the source of water (cooling tower, tap water, sea water, dry cooler, etc.). Water out depends on water in and should normally be within +5°K to +10°K from water in
    2) heat of rejection is cooling capacity plus power input of the compressor
    3) condensing temperature is normally +5°K to +10°K from water out temperature
    4) delta T, see above
    5) yes, there are limitations depending on the pressure drop of the tube bundle. The lower the DT, the higher the pressure drop. Pressure drop should not exceed 50/60kPa
    6) water flow depends on DT and heat rejection.

    But for a 15kW condenser I would prefer a PHE

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Thumbs up Re: HELP PLZ: Shell & Tube Selection Parameters

    Hello Mahmoud,

    Not easy to help but:

    Please, try to visit this page and download selection program:

    http://www.flatplate.com/downloads/

    or come here and check for literature:

    http://www.flatplate.com/literature.htm

    Hope you'll find what your'e looking for

    Seems very interesting site for other RE guys

    Come back with comments

    Best regards,

    Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Raj Pujar's Avatar
    Raj Pujar Guest

    Re: HELP PLZ: Shell & Tube Selection Parameters

    Hi Mahmoud,

    The italian is right on the money,

    When selecting condensing temperature add your temperature difference(TD) across the coil to the ambient temperature.ie, Ambient+TD=Condesing Temp
    Depending on the client and application the TD varies from +5K to +10k

    Delta T is = Condensing Temp - Liquid Temperature
    This is useful when you using PHE.

    I hope this would help you.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: HELP PLZ: Shell & Tube Selection Parameters

    Hello Josip,

    The person is interested in information a shell & tube condenser. Flatplate has PHEs. Standard Refrigeration, USA and Alfa Laval, has some good information on Shell & Tube Condenser. I feel nonickname has answered all the informations.

    Where are you now?

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: HELP PLZ: Shell & Tube Selection Parameters

    Hi, Samarjit Sen

    Quote Originally Posted by Samarjit Sen View Post
    Hello Josip,

    The person is interested in information a shell & tube condenser. Flatplate has PHEs. Standard Refrigeration, USA and Alfa Laval, has some good information on Shell & Tube Condenser. I feel nonickname has answered all the informations.

    Where are you now?
    .......that is one old post, hope he succeed.....it is not so difficult when you have so many friends here on RE forums...

    Back home, some small jobs around and rest

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Similar Threads

  1. Capillary Tube Selection
    By lana in forum Commercial
    Replies: 17
    Last Post: 12-03-2009, 05:57 PM
  2. shell and tube temps ?
    By old gas bottle in forum Industrial
    Replies: 20
    Last Post: 28-07-2006, 07:17 AM
  3. Procedure For Selection Of Capillry Tube
    By AMARNATH JHA in forum Fundamentals
    Replies: 6
    Last Post: 26-06-2006, 04:57 AM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  5. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •