    Sep 2004
    Dubai - United Arab Emirates
    38
    37
    HELP PLZ: Shell & Tube Selection Parameters
    Dear All,,
    Please help me out to start selection of shell and tube water cooled condensors in order to match it with refrigeration compressors, to make things systamatic and smooth for you i have some parameters am thinking about in mind:
    1- Water In/Out
    2- Heat of rejection (how can this be related to refrigeration capacity?)
    3- Condensing temp. (related to water In/Out).
    4- what is the appropriate delta T (Out-In), and what is the standard value.
    5- what is the minimum water in temp.?? is there any limitations ? ofcourse not close to zero.
    6- what is the appropriate water flow and speed for a selected condenser.
    actualy my case that i want to have 15Kw refrigeration @Tsuction -5c, which cond. temp. i shall go throw to select a compressor, and which water in temp. i have to consider, and whicg DT is applicable. in site i have from 15 to 20c water temperature to feed the condensors.
    i have noticed that all the manufacturers are stating the refrigeration capacities at 40c cond.
    i know it is too much questions, but it is the first time to use water cooled condensing units
    please your help.
    Thank you..
    Too Much Of Something Is Bad Enough
    Mar 2006
    Merate (LC) - Italy
    2,553
    Re: HELP PLZ: Shell & Tube Selection Parameters
    1) water in depends on the source of water (cooling tower, tap water, sea water, dry cooler, etc.). Water out depends on water in and should normally be within +5K to +10K from water in
    2) heat of rejection is cooling capacity plus power input of the compressor
    3) condensing temperature is normally +5K to +10K from water out temperature
    4) delta T, see above
    5) yes, there are limitations depending on the pressure drop of the tube bundle. The lower the DT, the higher the pressure drop. Pressure drop should not exceed 50/60kPa
    6) water flow depends on DT and heat rejection.
    But for a 15kW condenser I would prefer a PHE
    Jan 2006
    Croatia
    2,121
    23
    Thumbs up Re: HELP PLZ: Shell & Tube Selection Parameters
    Hello Mahmoud,
    Not easy to help but:
    Please, try to visit this page and download selection program:
    http://www.flatplate.com/downloads/
    or come here and check for literature:
    http://www.flatplate.com/literature.htm
    Hope you'll find what your'e looking for
    Seems very interesting site for other RE guys
    Come back with comments
    Best regards,
    Josip
    Raj Pujar's Avatar
    Raj Pujar Guest
    Hi Mahmoud,
    The italian is right on the money,
    When selecting condensing temperature add your temperature difference(TD) across the coil to the ambient temperature.ie, Ambient+TD=Condesing Temp
    Depending on the client and application the TD varies from +5K to +10k
    Delta T is = Condensing Temp - Liquid Temperature
    This is useful when you using PHE.
    I hope this would help you.
    May 2006
    India
    1,016
    13
    Hello Josip,
    The person is interested in information a shell & tube condenser. Flatplate has PHEs. Standard Refrigeration, USA and Alfa Laval, has some good information on Shell & Tube Condenser. I feel nonickname has answered all the informations.
    Where are you now?
    Jan 2006
    Croatia
    2,121
    23
    Hi, Samarjit Sen
    Quote Originally Posted by Samarjit Sen View Post
    Hello Josip,
    Where are you now?
    .......that is one old post, hope he succeed.....it is not so difficult when you have so many friends here on RE forums...
    Back home, some small jobs around and rest
    Best regards, Josip
  1. Capillary Tube Selection
    By lana in forum Commercial
    Last Post: 12-03-2009, 06:57 PM
  2. shell and tube temps ?
    By old gas bottle in forum Industrial
    Last Post: 28-07-2006, 07:17 AM
  3. Procedure For Selection Of Capillry Tube
    By AMARNATH JHA in forum Fundamentals
    Last Post: 26-06-2006, 04:57 AM
  4. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 07:57 AM
  5. The amazing Mr. Cap Tube