Results 1 to 10 of 10
    May 2014
    Moskow
    22
    Chiller YORK YCIV0840 Baseplate
    Hello all
    chiller York YSIV0840
    Faulty pump glycol
    The display shows: SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.
    Please, provide technical support and help
    Sincerely, Anatoly
    May 2014
    Moskow
    22
    Re: Chiller YORK YCIV0840 Baseplate
    amendment YCIV0840SA50VAB
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    Hi Anatoly
    Is your glycol pump ok? Check glycol level.
    Check the cabinet fan or you may have a faulty sensor
    May 2014
    Moskow
    22
    Hi hookster
    The pump is faulty.
    It was the starting block with a broken pump.
    Tell me where the sensor?
    What are the terminals connected?
    Do I need to manually reset this accident?
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Quote Originally Posted by *****959 View Post
    Hi hookster
    The pump is faulty.
    you said already the glycol pump is faulty.i dnt know what type of pump fault. repair or replace it.
    May 2014
    Moskow
    22
    amendment SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.
    May 2014
    Moskow
    22
    The pump is already engaged may replace a new one
    problem
    Display Indication Sus1 BLOCK: HIGH TEMPERATURE IRR baseplate.
    Removing the accident and where the temperature sensor
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    "Removing the accident"cannot understand. what is the glycol level? if glycol level is low, base plate temp will go high.
    May 2014
    Moskow
    22
    circuit status off
    where the temperature sensor is installed
    Apr 2010
    Qatar
    43
    28
    Leave sensor location it is on PCB you can not do anything...... If u replaced Glycol pump just topup glycol.......untill overflow then close cap.