    McQuay Microtech 100



    Hello everyone. I'm working on a McQuay centrifugal chiller with microtech 100, and has the following problem: by changing the chilled water temperature (LWT), and hit the enter the new value is accepted, but after a few seconds, the old value returns. That is apparently the new value is not saved as it should. anyone know the reason and the solution ?



  2. #2
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: McQuay Microtech 100

    Is there a minimum set point parameter that stops the set point being lowered

  3. #3
    ALBA's Avatar
    ALBA Guest

    Re: McQuay Microtech 100

    Hi fellow. The actual set point is 6.0C, and a trying to set in 7.0C.

  4. #4
    ALBA's Avatar
    ALBA Guest

    Re: McQuay Microtech 100

    Resolved. I found connected to the equipment a Jonshon controls controller, who thought no longer in use, but it's who made it impossible to exchange the LWT. After removed LLLB connection everything worked ...