    Emergency stop on compressor



    A client we work for has a number of Industrial compressors, on a number of sites.
    An opposition company did the install's.
    If you press local compressor emergency stop, the whole plant shunt trips!
    Is this crazy (I think) or is it the norm in some plants or countries?

    We sometimes during servicing press emergency stop if carrying out oil filter change etc , not at this place though.



  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Emergency stop on compressor

    The stop right now button on a compressor panel should not be an E-Stop for the plant. Lots of codes require E-Stops that halt all the machine room equipment and have specifics concerning location of the switch: Typically outside the machine room.....

  3. #3
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Emergency stop on compressor

    It seems odd to me. Related machinery, and perhaps any powered stuff within a few metres (having first come across them in engineering workshops, e-stops to me are as much about injury avoidance as anything). But what would the benefit of stopping the entire plant be?

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Emergency stop on compressor

    .

    I think there are at least two reasons to have an emergency stop button
    and the most common would be the one that is used locally to the machine,
    that stops that individual machine in the event of an emergency with it.

    The stop for the whole plant is a different issue and if done wrong could actually
    cause more problems than it would prevent, pressure rise in the wrong part of
    the system for one.

    So in my opinion emergency stops are used for the actual machine itself and if one
    is used for the whole plant, then it should be located near emergency doors and the
    main control panel.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..