    Chemical wash on condenser of chilleers



    Hi,
    Anyone has experience on chemical wash on condenser of chiller please advise.
    I would like to know the points to be aware of and precautions need to know etc.
    The chiller concerned is Ebara with plates design.
    Thanks



  2. #2
    Join Date
    Sep 2012
    Location
    India
    Posts
    77
    Rep Power
    13

    Re: Chemical wash on condenser of chilleers

    Weak solution of sulfamic acid at a temperature around 50 deg C helps to clear the scales. This should be following by circulation of caustic solution.

  3. #3
    Join Date
    Aug 2009
    Location
    Singapore
    Age
    47
    Posts
    42
    Rep Power
    0

    Re: Chemical wash on condenser of chilleers

    Hi Sandybapat, Is it for Air-cooled or water cooled chiller ? Thanks !

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chemical wash on condenser of chilleers

    this stuff is pretty efficient if it's on the water side
    http://wssproducts.wilhelmsen.com/ma...escalex-25-kg/

    http://wssproducts.wilhelmsen.com/ma...g-liquid-25-l/

    Both of these require you to circulate the mixture on the heat exchanger.
    We find it very effective on plate heat exchangers, but remember to circulate the mixture counter to normal flow

    According to the product guy I spoke to a few years back, it's not a marine pollutant and can be flushed to sea after use.
    for a closed system follow the neutralizing instructions, for a system open to the sea, just run the condenser pump for 5 hours to remove all residue
    -Cheers-

    Tycho

  5. #5
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    88
    Rep Power
    15

    Re: Chemical wash on condenser of chilleers

    Quote Originally Posted by Tycho View Post
    this stuff is pretty efficient if it's on the water side
    http://wssproducts.wilhelmsen.com/ma...escalex-25-kg/
    Holy crap! I'd not let that anywhere near my brazed plate heat exchangers. It's almost all hydrochloric acid. The chloride corrosion of the copper brazing would be terrible.

  6. #6
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Chemical wash on condenser of chilleers

    Quote Originally Posted by BradC View Post
    Holy crap! I'd not let that anywhere near my brazed plate heat exchangers. It's almost all hydrochloric acid. The chloride corrosion of the copper brazing would be terrible.
    oops, not to be used near brazed heat exchangers

    Good thing it said so in the product pamphlet *whew, dodged a bullet there*
    -Cheers-

    Tycho