    May 2009
    Singapore
    11
    Chemical wash on condenser of chilleers
    Anyone has experience on chemical wash on condenser of chiller please advise.
    I would like to know the points to be aware of and precautions need to know etc.
    The chiller concerned is Ebara with plates design.
    Sep 2012
    India
    77
    7
    Re: Chemical wash on condenser of chilleers
    Weak solution of sulfamic acid at a temperature around 50 deg C helps to clear the scales. This should be following by circulation of caustic solution.
    Aug 2009
    Singapore
    42
    42
    Hi Sandybapat, Is it for Air-cooled or water cooled chiller ? Thanks !
    Jan 2006
    Norway
    40
    801
    4
    22
    this stuff is pretty efficient if it's on the water side
    http://wssproducts.wilhelmsen.com/ma...escalex-25-kg/
    http://wssproducts.wilhelmsen.com/ma...g-liquid-25-l/
    Both of these require you to circulate the mixture on the heat exchanger.
    We find it very effective on plate heat exchangers, but remember to circulate the mixture counter to normal flow
    According to the product guy I spoke to a few years back, it's not a marine pollutant and can be flushed to sea after use.
    for a closed system follow the neutralizing instructions, for a system open to the sea, just run the condenser pump for 5 hours to remove all residue
    -Cheers-
    Tycho
    Oct 2010
    Australia
    88
    9
    Quote Originally Posted by Tycho View Post
    Holy crap! I'd not let that anywhere near my brazed plate heat exchangers. It's almost all hydrochloric acid. The chloride corrosion of the copper brazing would be terrible.
    Jan 2006
    Norway
    40
    801
    4
    22
    Quote Originally Posted by BradC View Post
    oops, not to be used near brazed heat exchangers
    Good thing it said so in the product pamphlet *whew, dodged a bullet there*
    -Cheers-
    Tycho
