minimum length pipe run between indoor and outdoor on mitsubishi heavy industry
Hi guys , installing a split mitsubishi heavy industry , outdoor unit FDT140VF , indoor unit cassette FDC140VN, what is the minimum pipe length between indoor and outdoor unit? may need to recover some refrigerant out of the system.
-
20-05-2015, 10:41 PM #2
Re: minimum length pipe run between indoor and outdoor on mitsubishi heavy industry
Can't see anything written down in their tech manual....
http://www.manualslib.com/manual/850...age=149#manualBrian - Newton Abbot, Devon, UK
Retired March 2015
-
22-05-2015, 10:20 PM #3
Re: minimum length pipe run between indoor and outdoor on mitsubishi heavy industry
with some units the short pipe run causes water droplets from the evap surface ; if you retired you may not need to know the manufactures brand, if you think the liquid remains in the liquid receiver or the condenser, with certain units that does not comply, what i ment was the distance to be less than 2m.
thanks for the reply????????????????
-
23-05-2015, 08:51 AM #4
Re: minimum length pipe run between indoor and outdoor on mitsubishi heavy industry
only small splits under 5kw highlight a minimum of 1.5mtr run- shouldnt matter on a mhi as the lev will control the superheat , best practice is to RTFM