    MC Quay (McEnergy AXN Chiller problem)



    My respectful colleagues,
    Hope all are good.
    I have air cooled McQuay chiller type McEnergy A 166.2 XN 134.
    the chiller shows the alarm " #1 EXV not closed during power OFF ".
    Then when go to unit setting system 1 expansion valve shows other message " EXV setting #1 system's waiting for valve open restart go a head ? N."
    If you please open the attached images with my thread.
    I changed the battery ( the battery was not good) and checked the EXV motor which is working fine.
    I checked the Carel's EXV driver. the LEDs are showing that " the valve open in case of lack of supply"
    ( LED open: flashing/ LED close: flashing / LED power: ON / LED alarm : flashing ).
    I need the Tech Password" to restart the EXV again.
    The password consist of 10 separate digits. (00000 00000).
    Hope someone will help and I'll be appreciated.
    Wish you all good day.

    Attached Images Attached Images



  2. #2
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    87
    Rep Power
    13

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hi can you try 40130-40145 please, or press + = - help. And may I ask are there any side effects of this problem to the system other than the fault code?
    Martin

  3. #3
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Thanks Martin,
    Side effects, the battery wasn't good and also alarm B6 the high pressure transducer.
    Saturday I'll try your password.
    By the way, I know the keys +/ - but the mark = don't have or know about it.
    Regards.

  4. #4
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    87
    Rep Power
    13

    Re: MC Quay (McEnergy AXN Chiller problem)

    Is the unit still running ok or switched off? And is there also a solenoid valve fitted?
    Martin

  5. #5
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hi Martin.
    System #2 still running but the system #1 stopped by the alarms "EXV. not closed during power OFF" and " EXV #1 battery error". There are solenoid valves for the economizer and capacity control on the compressor only and there is no S.V before the EXV.

  6. #6
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    87
    Rep Power
    13

    Re: MC Quay (McEnergy AXN Chiller problem)

    From what I've read about this online and other forums it sounds like you might have trouble accessing the controller without knowing the specific password and some controls are only accessible through a mcquay engineer with a laptop and software but good luck!
    Martin

  7. #7
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: MC Quay (McEnergy AXN Chiller problem)

    01331 07211

  8. #8
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Thanks Martin for your support.

    Quote Originally Posted by Martin Davies View Post
    From what I've read about this online and other forums it sounds like you might have trouble accessing the controller without knowing the specific password and some controls are only accessible through a mcquay engineer with a laptop and software but good luck!

  9. #9
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Thanks >>>> I'll check the password. With regards.
    Quote Originally Posted by RusBuka View Post
    01331 07211

  10. #10
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hi Martin, Rus
    I entered the passwords but they did not give access.
    Hope I can find new more password.
    I just want to give the order "YES" to make restart for the EXV. to verify again the zero point.
    Thanks anyway. I'll not stop and try more and more.

  11. #11
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: MC Quay (McEnergy AXN Chiller problem)

    heh you need new firmware)

  12. #12
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    15

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hamooody, try another one 1331721125

  13. #13
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Thanks Alex. I tried this before, and no response to it.
    Quote Originally Posted by AlexG View Post
    Hamooody, try another one 1331721125

  14. #14
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Rus, Tell me;How do you that??
    Quote Originally Posted by RusBuka View Post
    heh you need new firmware)

  15. #15
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: MC Quay (McEnergy AXN Chiller problem)

    Remove old firmwire and load new) But you need to kick some ass in McQuay., whey dont give firmwires to anyone.
    Soft for that operations you can find on KSA. Carel.
    But if you never do it, dont try))

  16. #16
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hi Rus,
    Today I tried another way to get an access to the tech. password. It is work fine and later I used your password and it works. Thanks to you for inspiring me to find the correct way.
    So, here let me also thanks Mr. Martin and Alex. Have good day.
    Quote Originally Posted by RusBuka View Post
    Remove old firmwire and load new) But you need to kick some ass in McQuay., whey dont give firmwires to anyone.
    Soft for that operations you can find on KSA. Carel.
    But if you never do it, dont try))

  17. #17
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: MC Quay (McEnergy AXN Chiller problem)

    You put new firmwire.?

  18. #18
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: MC Quay (McEnergy AXN Chiller problem)

    Hi Rus,
    No, I went to manager level and I entered the operator access password "100", then go to technical password I pushed up and down arrow together to rest the password. Later I entered your password and then I got access to technical level. Turn the letter N to Y " yes" the problem solved EXV worked but still need to change the EXV driver battery though the old battery read 18 volt dc. but the controller generate the alarm " EXV.#1 driver battery error". And when I use the other system's battery the alarm gone . Nice day
    Quote Originally Posted by RusBuka View Post
    You put new firmwire.?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments