    Howto: Calculate coaxial heat exchangers



    Can someone point out some technincal articles on how to calculate heat transfer in coaxial heat exchangers using R404A refrigerant and seawater.



  2. #2
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: Howto: Calculate coaxial heat exchangers

    you mean the tube in tube heat exchanger?
    I hear...I forget;I see...I remember;I do...I understand

  3. #3
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Howto: Calculate coaxial heat exchangers

    The same basic principles apply to all heat exchangers.

    Best is the e-Ntu method. Reason is that there is no iteration so is ideal for hand calculation.

    There are 3 simultaneous equations to solve.

    1. Heat transfer from hot fluid to cold fluid.
    Q = e Qmax
    e = effectiveness
    Qmax = (mc)min x ITD
    ITD = inlet temperature difference
    (mc)min = min capacity rate
    read e from e-Ntu curve
    where Ntu = UoAo/(mc)min

    2. Hot fluid energy loss
    Q = (m Cp dT)hot

    3. Cold Fluid energy loss
    Q = (m Cp dT)cold

    Note that Q is the same in each equation. Implies that heat lost from hot fluid = heat gain by cold fluid.

    This is standard textbook stuff, you will find it in Holman or any other heat transfer text book. There is a very good book that is available for free download by Prof Lienhard at MIT.
    http://web.mit.edu/lienhard/www/ahtt.html


    The South African Institute of Refrigeration and Air Conditioning (SAIRAC), has a technical data CD that will cost you about $100.
    www.sairac.co.za

  4. #4
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Howto: Calculate coaxial heat exchangers

    Quote Originally Posted by nh3simman View Post
    Best is the e-Ntu method. Reason is that there is no iteration so is ideal for hand calculation.
    There are 2 heat exchanger solve methods:

    1. Effectiveness method
    2. LMTD method

    They are theoretically equivalent, so you can use either.

    I'm not fan of LMTD because it requires iteration. It goes like this:

    Q = Uo Ao LMTD

    Seems simple on the face of it but the LMTD demands the knowledge of both fluid leaving temperatures.

    See the paradox here?

    If you know the leaving temperature of any of the fluids then you have the answer.

    The LMTD method is good for selectors where the temperatures are specified and you need to calculate the coil size.

    Where the LMTD method fails, is on cooling coils where you have condensation. This means 2-phase heat transfer and so the temperature difference is not the driving force (the driving force in this case is the enthalpy difference). On the other hand, the effectiveness method does not suffer from this problem since Qmax can easily by defined in terms of the enthalpy difference.

    eg. for DX coil
    Qmax = (mc)min x (hai - hswi)
    hswi = enthalpy of saturated air at suction temp.


    I have published an article on this subject that can be read on my web site. It is freely available to read on-line. If you would like to read it, I will send you a link privately (apparently you get suspended by ANDY if you post links)

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Howto: Calculate coaxial heat exchangers

    Hi, nh3simman


    Quote Originally Posted by nh3simman
    I have published an article on this subject that can be read on my web site. It is freely available to read on-line. If you would like to read it, I will send you a link privately (apparently you get suspended by ANDY if you post links)
    I think you can make a link in your profile (go to User CP - Home page URL) to your web page and we all can read your article

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Howto: Calculate coaxial heat exchangers

    Quote Originally Posted by nh3simman View Post
    ..........I have published an article on this subject that can be read on my web site. It is freely available to read on-line. If you would like to read it, I will send you a link privately (apparently you get suspended by ANDY if you post links)
    You will suspended by ANY moderator for posting adverts, links we don't mind but you were pushing your site quite a lot.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Howto: Calculate coaxial heat exchangers

    Quote Originally Posted by nh3simman View Post
    eg. for DX coil
    Q=eQmax
    Qmax = (mc)min x (hai - hswi)
    hswi = enthalpy of saturated air at suction temp.
    Good information, simman.
    I regard this method just be suitable to estimate, not the exact calculation. how to get the value of "e"? it is based on many factors such as tube material, flow configuration etc. This kinds of calculation always depend on some empirical formulas.

  8. #8
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Howto: Calculate coaxial heat exchangers

    Quote Originally Posted by ernestlin View Post
    Good information, simman.
    I regard this method just be suitable to estimate, not the exact calculation. how to get the value of "e"? it is based on many factors such as tube material, flow configuration etc. This kinds of calculation always depend on some empirical formulas.
    Hi ernestlin,

    The effectiveness is no estimate, in fact it can be derived directly from the LMTD method.

    e comes from the e-Ntu curve.
    where Ntu is the number of transfer units.
    Ntu = UoAo/Cmin
    Ao and Cmin are known values.

    The unknown is Uo (the overall heat transfer coefficient), and here I must agree with you.

    Uo can be calcuated from the many well known correlations or it can be based on manufacturers data.

    But the uncertainty in Uo applies equally to the e-Ntu method or the LMTD method.

    My point is that in calculating the duty of an existing heat exchanger, the e-Ntu method has huge benefits in terms of calculation speed. In addition, the e value is bounded by 0-100% so your calculations cannot diverge.

    In any event, you can easily calculate with one method and compare with the other.

  9. #9
    Join Date
    Jan 2008
    Location
    Durban
    Age
    37
    Posts
    21
    Rep Power
    0

    Re: Howto: Calculate coaxial heat exchangers

    Hi nh3simman,

    I know this is an old thread, but I've recently been looking into coaxial heat exchangers, could you please go through an example to give a better understanding,
    please don't take offence but I'm a hands on kind of guy and nomenclature's make my brain basically freeze when I dont have a grasp of where the figures are coming from.

    Say if we have a 3/4" tube for the refrigerant side and a 1/2" tube as the inner water side, using any flow of choice on both the refrigerant side and water side, and all other necessary values, how can we work out the capacity of a 1 meter length?
    in lamens terms would be helpful


    I would really appreciate your knowlege input on this as I've been struggling to find answers for quite some time

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Howto: Calculate coaxial heat exchangers

    Have you tried coolpack? You can easily calculate heat exchange on liquid or gas pipes.

  11. #11
    Join Date
    Jan 2008
    Location
    Durban
    Age
    37
    Posts
    21
    Rep Power
    0

    Re: Howto: Calculate coaxial heat exchangers

    Hi NoNickName,

    Just downloaded coolpack, using the liquid and gas pipe modules, but I don't see how it can help me because I want to run refrigerant on the outside tube and water on the inside, so the outside tube volume would be the difference beween the two and the surface area would be the water side tube.

    I was hoping nh3simman would go through a working example since he obviously knows what he's doing

    Most school testbooks didnt just give you a formula, they gave you an example to show how to use it.

    Would be great to set up a little excel spreadsheet where I could plug in my figures and play around with the values, rather than re start each time.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Howto: Calculate coaxial heat exchangers

    It works, if you know how to bend it to your needs. Calculate the two things separately.

  13. #13
    Join Date
    Jan 2008
    Location
    Durban
    Age
    37
    Posts
    21
    Rep Power
    0

    Re: Howto: Calculate coaxial heat exchangers

    so whats step 1 ?

    I've never used coolpack before,
    where would you start?

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Howto: Calculate coaxial heat exchangers

    Step 1 is data input. Please give input.

  15. #15
    Join Date
    Jan 2008
    Location
    Durban
    Age
    37
    Posts
    21
    Rep Power
    0

    Re: Howto: Calculate coaxial heat exchangers

    say we're working with a condenser,
    the condenser outer (refrigerant) tube is 1 1/8" with 1mm Wall thickness.
    and the inner (water) tube is 5/8" also with 1mm Wall thickness.

    the water in temperature is at 30degC
    with a flow of about 1L a second.

    on the gas side, 404A the inlet temperature is 60 deg at 400psi (+-2700kPa)

    the overall tube assembly length is 5 meters.

    what else do you need?

Similar Threads

  1. Refrigerant to water heat exchangers
    By sunwind in forum Technical Discussions
    Replies: 20
    Last Post: 24-06-2008, 01:40 PM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Poor Heat Exchangers
    By alireza in forum Trouble Shooting
    Replies: 9
    Last Post: 21-03-2007, 09:51 PM
  4. Where to buy coaxial heat exch. for refrigeration.
    By JKProSoft in forum Technical Speculations
    Replies: 4
    Last Post: 26-04-2006, 08:39 PM
  5. Help to calculate Heat Exchancger
    By Carode in forum Fundamentals
    Replies: 1
    Last Post: 17-12-2003, 11:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •