    Question oil dilution+high pressure and temp.



    Hi, I would appreciate any input on this observation I made.
    A scroll compressor that works with R-22 was vibrating during operation a bit more than normal. This caused the pipes to break. I noticed that the heat pump was operating on heat at 24-25 bar discharge pressure due to dirty, blocked air filters. My opinion is that that the oil in the faulty compressor was diluted due to working at high pressure and temperature for 18 months. This resulted in the eventual breakdown of the compressor which resulted in the vibration.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: oil dilution+high pressure and temp.

    I don't think I would call this a dilution problem. This occurs when the oil has liquid refrigerant in it. The oil viscosity is lowered when the refrigerant is mixed with the oil.

    In your example the oil viscosity was decreased by the high temperatures due to the air flow restriction. In addition to the lower oil viscosity issue the higher operating pressures would apply additional forces to the compressor bearings and other lubricated parts.

  3. #3
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: oil dilution+high pressure and temp.

    Thanks for your input Iceman. I meant the viscosity but my English was incorrect. Thanks for pointing it out.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: oil dilution+high pressure and temp.

    I personally think that the chemical engineers make that the oil holds it lubrification capacities while working under different conditions.
    24 to 25 bar (348/362 psi) is high but is for the oil not such a big deal.
    Oil can decompose as soon discharge temperature reaches 140°C (284°F)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19

    Re: oil dilution+high pressure and temp.

    24bar? Blimey. You could have had some air in there, raising the head pressure and making the compressor have to work very hard, hence the vibrations.
    It's a lovely day to pump some gas

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. GSHP discharge temp high
    By Lc_shi in forum Trouble Shooting
    Replies: 6
    Last Post: 20-01-2005, 09:37 AM
  3. Noobie question.Evaporator Pressure.
    By kfjoe in forum Fundamentals
    Replies: 8
    Last Post: 04-03-2003, 10:11 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •