    Question Carrier 30AX help needed



    Hi Guys,

    i have this weird alarm "low economizer pressure", after runing the compressor 5 minutes the economizer pressure is dumping less then the suction pressure by 15 psi and then the alarm is set. I replace the EXV valves and the dryer elements... nothing helps.

    I have enough gas in the system since the suction pressure is by the book.

    i also have a problem that the compressor is not realy loading to full capacity, the controler shows that the compressor is loading but the pressures and the amps remain the same...Oil pressure is fine so i am clueless

    can anyone help?

    Thanks In advance
    Tamir



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Carrier 30AX help needed

    Hi Bukichu1
    Welcome to the forum!
    If you mean a 30 XA then your fault is either.
    Faulty transducer or High Pressure Switch or Low/Restricted Condenser Flow!

    Given that it is not loading correctly I would check the transducer first.
    Grizzly
    Last edited by Grizzly; 11-05-2015 at 10:07 PM.

  3. #3
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Carrier 30AX help needed

    Hi good afternoon:

    lugtar checaria first economizer the transducer is not damaged.
    revised second solenoid compressor if they are energizing.

    reviews all sensors especially the environment