    Angry interlevin 1 metrer dairy cabinet



    Having a problem with a dairy cabinet,every 2 Weeks it freezes up, have checked gas R 404 pressures ok comes down to temperature then cuts out at aquired temp,cut back in at required temp, cut it possibly be the expansion valve flooding evaporator?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: interlevin 1 metrer dairy cabinet

    What state is the unit in?

    How are they using it?

    May not be a gas problem.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: interlevin 1 metrer dairy cabinet

    Had this with a 12ft case - 1 half worked OK but the other half continually iced the evap.

    Moved the control sensor to cure it.

  4. #4
    Join Date
    Jan 2009
    Location
    uk
    Posts
    12
    Rep Power
    0

    Re: interlevin 1 metrer dairy cabinet

    Thank you for replying Frank have moved probe but continues to ice up,I think i will change the controller see if that works.

  5. #5
    Join Date
    Jan 2009
    Location
    uk
    Posts
    12
    Rep Power
    0

    Re: interlevin 1 metrer dairy cabinet

    its about 6years old in great nick,I have recently replaced evap fan and also condensor fan,gas is ok moved probe to see if that helps but 10 days later its back in really frustrating as they are nice people.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: interlevin 1 metrer dairy cabinet

    Sometimes, customers place products inside the cabinet so they disturb the air movement.
    If evaporator is at the bottom, check for dirt that might block the air.

    Is there any head pressure control?

  7. #7
    Join Date
    Jan 2009
    Location
    uk
    Posts
    12
    Rep Power
    0

    Question Re: interlevin 1 metrer dairy cabinet

    Quote Originally Posted by chemi-cool View Post
    Sometimes, customers place products inside the cabinet so they disturb the air movement.
    If evaporator is at the bottom, check for dirt that might block the air.

    Is there any head pressure control?
    Hi chemi-cool,
    evaporator clean, no hp/lp unit comes down to +3 degrees cuts off then comes back in at +10 degrees it takes about 10 days then it freezes the milk, called out and it was - 9 degrees unit not cutting out, refrigerant charge ok, expansion valve seems to be operating correctly,mmay change the controller and probe.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: interlevin 1 metrer dairy cabinet

    Quote Originally Posted by refrep View Post
    Hi chemi-cool,
    evaporator clean, no hp/lp unit comes down to +3 degrees cuts off then comes back in at +10 degrees it takes about 10 days then it freezes the milk, called out and it was - 9 degrees unit not cutting out, refrigerant charge ok, expansion valve seems to be operating correctly,may change the controller and probe.
    In that case, I'd go with Frank!

  9. #9
    Join Date
    Jul 2009
    Location
    essex
    Age
    47
    Posts
    19
    Rep Power
    0

    Re: interlevin 1 metrer dairy cabinet

    Have they got air cond blowing into the case I've had this before just a suggestion

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: interlevin 1 metrer dairy cabinet

    Quote Originally Posted by refrep View Post
    Hi chemi-cool,
    evaporator clean, no hp/lp unit comes down to +3 degrees cuts off then comes back in at +10 degrees it takes about 10 days then it freezes the milk, called out and it was - 9 degrees unit not cutting out, refrigerant charge ok, expansion valve seems to be operating correctly,mmay change the controller and probe.
    Was your sub zero temperature reading consistent for the entire cabinet? Left side, Middle and the far end?
    Has to be the probe or Controller fault if all readings are similar. Whether it be an electronic or mechanical controller, set it for maximum temperature, just to see if condensing kit shuts down.

    Check your superheat.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: interlevin 1 metrer dairy cabinet

    Sounds like a faulty controller, or leaky solenoid if its on pumpdown.
    Mostly found in Oxfordshire, UK :)

  12. #12
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: interlevin 1 metrer dairy cabinet

    Did you solve this Refrep? Possible liquid solenoid passing?