    trane chiller



    have a trane chiller with 2 compressors one compressor keeps tripping on phase imbalance other one working ok have checked run amps both comps drawing 37 41and 41 amps volts 220 225 and 225 any idears



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: trane chiller

    Swap the CT's and see if the fault moves across to the other compressor

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: trane chiller

    have tried that and still same comp tripping strange only one tripping as they both pull the same amps

  4. #4
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: trane chiller

    Hi Martin58
    Your voltage readings are exceeding the +_5% tolerance
    Have you checked all your terminal connections and contacts for wear? Swap over the starter modules and see if comp trip moves over.

    Then replace starter modules and check your supply voltage and supply cabling and switch circuit connection.
    I love the smell of Ammonia in the morning!

  5. #5
    Join Date
    Aug 2013
    Location
    Hampshire
    Age
    38
    Posts
    87
    Rep Power
    13

    Re: trane chiller

    What does it trip exactly? Breaker in DB?

  6. #6
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: trane chiller

    the manual states 15% tolerance. the unit brings fault up on controls not trip of breakers