    R600a/R134a



    Hello can you please advise. My Whirlpool Fridge Freezer has lost its charge R600a the compressor nearly cooked its,self but is still pumping model ACC HTK 12 AA.Could I use R134a and get reasonable temperatures with the existing compressor? Would it be possible to recharge the system without scales. I have done this in the past when in Africa squirting gas into the system to get some cooling coming back to the compressor
    Thank You Grump



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: R600a/R134a

    .

    Why not do it properly using the correct gas it was designed for?
    If the system has leaked out have you found the leak?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R600a/R134a

    Oil type is probably wrong for R134a, pressure are all wrong too. So that would be a no.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Dec 2007
    Location
    England
    Age
    82
    Posts
    74
    Rep Power
    17

    Re: R600a/R134a

    Quote Originally Posted by Rob White View Post
    .

    Why not do it properly using the correct gas it was designed for?
    If the system has leaked out have you found the leak?

    Rob

    .
    Thank you I am pretty sure the leak was on the crimp at the charging port, it was not welded I assume that was because of the R600 . I dont like the idea of using flammable gasses as a refrigerant
    In the meantime I agree the sensible thing to do would be to find the leak and use the proper gas
    I seem to be making a big deal out of the repair not used to domestic units.
    I can borrow all the gear to get it done but have never weighed in such a small amount of gas ,I have not found any information on the charge.
    Thank you for your good advice Grump (retired HVAC)

  5. #5
    Join Date
    Dec 2007
    Location
    England
    Age
    82
    Posts
    74
    Rep Power
    17

    Re: R600a/R134a

    Thank you ,Rob has advised me to find the leak and charge with the proper gas, went off off on a tangent when I found it was charged with R600 it reminds me of the saying" keep it simple stupid"
    Thank You Grump

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: R600a/R134a

    Hydrocarbon Fridges use Mineral oil. R134a runs with synthetic.

    Had a 3 door bench top display with a Compressor fault recently. R600a. I would have stuck my neck out and fitted a suitable R134a compressor if the original UK compressor model number search gave me the CC displacement. Sigh.