    Fujitsu split air conditioner unit Low side valve



    I have a new Fujitsu split unit. It was low on the refrigerant. When I'm trying to remove the gauge I'm getting a strong refrigerant pressure. The low side valve is in shut position. It turned all the way off. Now I can't remove the gauge. Do you think I have defective low side valve.
    Attached Images Attached Images
    Last edited by Bagel; 30-04-2015 at 07:28 PM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu split air conditioner unit Low side valve

    low side valve should be open! once installed an comissioned

  3. #3
    Bagel's Avatar
    Bagel Guest

    Re: Fujitsu split air conditioner unit Low side valve

    I really appreciate if you could give me some guideline. I assume I have defective nipple. But I don't know how to replace it. I have lots of pressure there. The refrigerant is 410A. As soon as I loosen the gauge hose adapter the refrigerant starts coming out under high pressure. If I still remove the hose adapter I'm running out of refrigerant.
    Thanks,

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fujitsu split air conditioner unit Low side valve

    There will always be pressure at the Schrader valve.

    Use a quick connector in future.

    What qualifications do you have to work on refrigerants?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Bagel's Avatar
    Bagel Guest

    Re: Fujitsu split air conditioner unit Low side valve

    Thanks for the reply. I'm EPA Universal Certified. We repair commercial refrigeration appliances and commercial bakery equipment.

  6. #6
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Fujitsu split air conditioner unit Low side valve

    with the valve closed the Schrader is open to the system close the valve on the expansion (liquid) line and pump the unit down to remove your gauge